Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to choose the cable size for 100A(is there any formula
please update)

Answers were Sorted based on User's Feedback



how to choose the cable size for 100A(is there any formula please update)..

Answer / k.prakashchandra

In usual practice, the carrying capacity of copper is taken
as 2.5 A/sq mm and 1.5 for Al.If the load is steady and
continuous 60 % of these values are adopted.

Is This Answer Correct ?    4 Yes 3 No

how to choose the cable size for 100A(is there any formula please update)..

Answer / jamil

According to NEC , i want to reduced grounding cable from
4mm2 to 2.5 mm2 ,can u give me technical sheet to depend it
from NEC

Is This Answer Correct ?    1 Yes 2 No

how to choose the cable size for 100A(is there any formula please update)..

Answer / hari

Cable size should be 25 Sq.mm

For Ex: 1000A MCCB
For Al - We have to Consider 0.8/Sq.mm
For Cu - We have to Consider 1.6/Sq.mm

For 1000A = 1000*0.8
= 800A
We have to go for (100X10)mm Bus Bar

Is This Answer Correct ?    3 Yes 5 No

how to choose the cable size for 100A(is there any formula please update)..

Answer / balraj.gabriel

There is no formula for calculating the cable size. Usually
the cables are sizing based on standards like NEC,BEC.,
etc. if you want to size the cable you first choose the
std, which is using in ur location.as per NEC std just
multiply the 100*1.25=125A, choose the cable ( table-
310.16) for that size. after you choose the cable you have
to derate the cable for your laying location & way of
laying.

Is This Answer Correct ?    1 Yes 3 No

how to choose the cable size for 100A(is there any formula please update)..

Answer / shirish

Theory for Cable Sizing.
From Ohms law, the voltage drop in an electrical conductor is
V = I R
where
I = Current, amps
R = Resistance, Ohms

The electrical resistance can be derived from the properties of the conductor material.
R = &#961; L / A
where
&#961; = Resistivity, &#937; mm2 /m
L = Length, m
A = Cross sectional area, mm2
Watch the units in the above equation.

The resistance can also be expressed in terms of the material conductivity (&#968;) which is just the reciprocal of the resistivity.
R = L / (&#968; A)

Table 1. Typical material electrical conductivity
Material Conductivity, &#968;
Copper 58
Aluminium 36
Mild Steel 7.7

Combining Ohms law with the resistance expression, we get.
V = (I L) / (&#968; A)

Now, we can define an acceptable voltage drop in a conductor. I have calculated the voltage drop that was used in several published tables and get around 5.5 Volts.
We could therefore re-arrange this equation to give the cable size. But cables come in standard sizes measured in mm2. In addition, you also need to consider the maximum current for each cable size.

Table 2. Conductor sizes and maximum currents
Cable Size, mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300
Maximum current, A 13 21 28 36 46 61 81 99 125 160 195 220 250 285 340 395
So, the theory is relatively simple, let us now see how to use the program.

Is This Answer Correct ?    0 Yes 2 No

how to choose the cable size for 100A(is there any formula please update)..

Answer / amrish sharma

there is no funda or formula to get size of conductor wrt
to load. just calculate the ampere of the load, and then as
per ampere ,,, as per the cross sectional area of the
conducter like 1.5mmsq can bear the 4-6amp load,,,so on..

Is This Answer Correct ?    4 Yes 16 No

Post New Answer

More Electrical Engineering Interview Questions

We are preparing another project which involves Waste heat recovery from a 1 MW GE Engine. The Engine in particular gives out flue gas at 487Deg C with a flow rate of 5650 kg/hour and this can be cooled to 180 Deg C. This gives a thermal output of ~ 594 KW that is available for input to VAM via heat exchanger / boiler. Additionally 581 KW will be available from engine jacket water (temperature profile 80/ 80 Deg C and a flow rate of 50m3/hr) Our estimation is that 300 TR of cooling is possible with a suitable VAM machine(s). Please advise what is the most suitable arrangement with maximum TR and min Capital expenditure. plz reply me as early as possible

0 Answers  


11 kV line deraction check by an Engineer.

0 Answers  


What is maximum permissible length of cable from transformer (33kV/0.433kV) HT side to HT panel which contain VCB? In which standard i shall get this information.

6 Answers   MSEB,


TYPES OF TEMPERING OF ENERGY METER

1 Answers  


What is UJT PNP, NPN transistor & working principles?

1 Answers   TATA,


what is bus pt and what is the function of it

2 Answers  


what is demagnetising effect & crossmagnetising effect and how it is related to electrical system?is there any more effects are available or only these two??

1 Answers   Telco,


how to find 5 kilo meter long under ground 33 kv cable fault location if IR VALUE shows 0.05 M ohm @5000 volt.and cable fault locator shows some time fault distance 3 kilo meter ,3.7 kilo meter and some time 1 kilo meter? now how to find the fault location that where is leakage. note--it is tested with 5000 kv megger and insulation resistance is 0.05 M ohm. and some time 0.03 M ohm comes.

0 Answers   OPS,


what is the MF if CT ratio is 500/5 and in meter specification is 3.75 REVS/KWH? Thanks and Regards Selvendran.N

1 Answers  


what are the main hormonics in ac?

1 Answers  


what is RTU with SCADA connection ?

2 Answers  


where is the primary of CT??

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)