How do you protect your appliances from harm in case of
neutral failure in a three phase power supply set up.
Answers were Sorted based on User's Feedback
Yes if neutral fails in a three phase power supply system
than the single phase voltage may increase. You can fix voltage sensitive suppressors across the supply line in your applances which will short circuit the excess voltage to earth and cause the RCCB to trip and save your appliances from further damage.
| Is This Answer Correct ? | 3 Yes | 0 No |
Whenever neutral fails in three phase system, the connected
loads will get connected between phases owing to floating
neutral.Hence depending on load resistance across these
phases, the voltage keeps varying between 230V to 400V.A
suitable servo stabilizer with wide input voltage range with
high & low cutoff may help in protecting the equipments.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / raj
Simply use ELCB or RCBO as incomer in the 3ph supply system
since if neutral opens it will trip the complete supply
without damaging to the system.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / lokesh ranjith
If nuetral fails in three phase system nuetral floats then
230 volts in will become 420V caused damage to the
equipment
| Is This Answer Correct ? | 2 Yes | 8 No |
what is earthing.how we make it,describe briefly.
what is S.D.F stands for ? (S.D.F unit 80 amp , TPN )
The power showed in the name plate of the motor is input power or output power?? The power showed in the name plate is 18.5kw measured current is 34.5 amps. location is india. can i calculate the efficiency of the motor using this data??
what is LUX?
Application wise, where we should use AC motors and where we should DC motors?
what convarts RRA in alternator ,AC to DC or DC to AC,
Is there a chance for a motor speed to become negative..?? What is the reason for such a phenomenon.? In that case does the motor works as a generator..???
How to megger test 11 kV cable and the acceptance IR value
How do you select a cable size(cu and Al) for a particular load
Can the same motor be operated in both direction ?
12.5 tons a/c is their how much kva generator can recommend to the customer.
why capacitors cant used in genset to maintain power factor..??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)