we have two 11/.433 kv. distribution Transformer rating as
1000 kva & 500 kva , i wants to run parallel both transformer.
both transformer impendence voltage is 5.24%, How can we run
both t/f, & how sharing the load
Answer Posted / virendra
As mentioned if the capacity, the vectror group ,
Impedance is equall you can connect both the transformet
in parrel just make sure that the Phase sequence for both
the transformer is same at the time of parallel & as the %
impedance is same the laad sharing will be equall.
| Is This Answer Correct ? | 0 Yes | 1 No |
Post New Answer View All Answers
How to identify the start and end of 3phase 12 lead motor if U1, U2, etc numberings are lost or erased.
What is the direction of current flow in ct secondary...means if the current is flowing from P1 to P2 then what will be the direction of current flow in ct secondaryw
explain the types of drives
Can 33kva/415v transformer be run underground? If the answer is yes why and if the answer is no why?
1.what is the difference between ct and cvt? 2.what is the difference between pt and cvt? 3.what is the difference between relays and circuit breakers?
I need the list of Universities who have summer intake for BS degree in Electrical Engineering.?
How to calculate the sag of OPGW during stringing???
we are having 110 Kv,250mA Electrostatic precipitators for coal fired boilers. what will be static voltage and current after discharge and what time it will remain before earthing?
How can we calculate ac current from the given DC current when AC voltage is given?
Can 4pole (3 phase+neautral )RCCB proper functioning in only 3 phase load (no neautral, no Earth) ?
What is CVT and what is relation with wave trap?
quantizer means?
What is meant by reactance voltage?
What are the two major types of control system?
-How do you select cable size for a given load at a given distance from source of supply. How do you find voltage drop.