A 150KW 440V motor is need to replace in the field instead
of faulty one. what are the main parameter should I need to
check?
150kw , 440 is a large motr. the starting current of this
induction motor will be 5-8 times depend on drive ex-fan.
and coast for 6-8s to attain full speed.
so, the new contactor shall be good quality , with
overload,instantaneous with time delay shall be selected.
Reverse rotation protection, vibrations,
Unbalnced current protection optional.
LV power cable terminal box cable connection and support.
Is This Answer Correct ? | 0 Yes | 0 No |
Can Anyone suggest the Standards (IEC or IS) for selecting copper current density?
how can we select the rating of Load break switch that is connected to the primary protection of 200 kva 11kv/415v distribution transformer?? step by step calculated answr pls...thnk.u
Please tell me ceilingfan sweep means. Commenly we used sweep1200mm and 600mm MMENLY WE USED CEILINGFAN SWEEP1200MM AND SWEEP600MM
what is ATS?and its function or operation in power system with its layout.
Why no-load primary current is very small as compared to full load current in transformer (as 1% of full load current?
what happens if dc supply is given and the remedies for it.
HOW TO CALCULATE SINGLE PHASE AMPERES IN 3 PHASE TRANSFORMER? GIVE AN EXAMPLE PLZZZ
HOW many type of Circut Breaker in the world used in 400 kv substation?
If I fill the form of engineering services and I left the exam de to navoidable reasons . Will it counts my one attempt
Why we are use 11KV / 22KV / 33KV / 66KV / 110KV / 230KV / 440KV this type of ratio. why cant we use other voltage ratio like 54KV / 99KV et.,
8 Answers College School Exams Tests, Hino, ITC Infotech, Reliance, UPRVUNL,
Please brief working principle & construction of permanent magnet AC Servo motor
Can we use generator transformer as step down transformer? How?