Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what is the maximum load on for 10 kva & 25 kva transformer

Answers were Sorted based on User's Feedback



what is the maximum load on for 10 kva & 25 kva transformer..

Answer / sandep

load is depend on p.f.
say pf=1 then load is=10kw and 25kw
for pf .9 then load is=9kw and 22.5kw

Is This Answer Correct ?    49 Yes 10 No

what is the maximum load on for 10 kva & 25 kva transformer..

Answer / aruloli

Dear Friend
You forgot to furnish few more data i.e Voltage rating of
primary and secondary.

If i assume Voltage rating for 10 KVA Transformer as 230
V/110 V (Primary/secondary)and considering as single phase .

primary load current is calculated as

P=VI

10*1000(VA)=230*I
I=43.47 A

Secondary current is ,
90.90 A

Considering Transformer as 3 phase, then

P=1.732*v*I

Primary load current is

10000=1.732*230*I

I=25.10 A

Secondary is,

52.48 A

Is This Answer Correct ?    35 Yes 15 No

what is the maximum load on for 10 kva & 25 kva transformer..

Answer / k.sri405

10 kva & 20 kva means transformer apparent power that is
combination of active and reactive power so we can load this
transformer below its rating coz load means only active
power .but in case of purely resistive losd we can load this
transformer upto its rating but practically purely resistive
load is not possible.

Is This Answer Correct ?    7 Yes 3 No

what is the maximum load on for 10 kva & 25 kva transformer..

Answer / kaleem

aroluli which voltage we'll use ? line to line to line to line to ground ?? 230 or 400 this formula to calculate 3 phase current ?? p= 1.73 v i cos@

Is This Answer Correct ?    3 Yes 1 No

what is the maximum load on for 10 kva & 25 kva transformer..

Answer / dkverma67

For 3phase transformer
10 KVA=10*1.4 Amp=10.4 Amps maximum
25 KVA=25*1.4 Amp=35.0 Amp max.

Is This Answer Correct ?    8 Yes 9 No

what is the maximum load on for 10 kva & 25 kva transformer..

Answer / pillay

the max load you already said as 10 kva and 20 kva. In terms
of kw it will be 10 & 2o kw also, so long it does not exceed
10 & 20 kva ampere ratings.

Is This Answer Correct ?    5 Yes 6 No

what is the maximum load on for 10 kva & 25 kva transformer..

Answer / ghannesh

hi all please remember in india 1 kva =1.33a then
10 kva = 13 ams use it only 80%load =13*.80=10.4 amp load
25kva*1.33=25 ams ams aprox we use 80% load 33.25*.80=26.6 a maximum load it is safty of trnsfomer

Is This Answer Correct ?    1 Yes 2 No

what is the maximum load on for 10 kva & 25 kva transformer..

Answer / velu5185

DEPENDS ON SEC. CURRENT

Is This Answer Correct ?    5 Yes 10 No

Post New Answer

More Electrical Engineering Interview Questions

how many frequent start/stop operation possible in case of HT MOTORS.

5 Answers   DVC, Steel Plant,


How many wall/floor flange will i use in bus duct system if we have in our design a 35th floor building.

0 Answers  


say a transformer is designed for 33/11kv step down with ratio 0.33 for load 1 mva. if am giving 11kv as a input that same transformer what will happen to its o/p voltage. and whether it can be operated for 500kva

4 Answers  


how we calculate the dick for a pole?

0 Answers   Power Grid,


If there is major % of Voltage harmonics in the system, how can it be control or reduced?

0 Answers   JCN, Wipro,


what is the meaning of osr in transformer.

0 Answers  


Write the analogous electrical elements in force current analogy for the elements of mechanical translational system.

0 Answers  


What is the mulplying factor of trivector meter (11kv) having ct ratio 100/5 amp.

2 Answers  


some meggers have three terminals. wat is the real function of the earth terminal?

2 Answers  


why in scott connection of transformers, main transformer is tapped at 50% and teaser transformer at 86.6%?

5 Answers   Bhel, Bosch, College School Exams Tests, Wipro,


When MICC cables used ?

0 Answers   Clinga,


DIFFERNCE BETWEEN DCS AND PLC? HOW IT WORKS?

0 Answers   Essar,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)