what is the maximum load on for 10 kva & 25 kva transformer
Answers were Sorted based on User's Feedback
Answer / sandep
load is depend on p.f.
say pf=1 then load is=10kw and 25kw
for pf .9 then load is=9kw and 22.5kw
Is This Answer Correct ? | 49 Yes | 10 No |
Answer / aruloli
Dear Friend
You forgot to furnish few more data i.e Voltage rating of
primary and secondary.
If i assume Voltage rating for 10 KVA Transformer as 230
V/110 V (Primary/secondary)and considering as single phase .
primary load current is calculated as
P=VI
10*1000(VA)=230*I
I=43.47 A
Secondary current is ,
90.90 A
Considering Transformer as 3 phase, then
P=1.732*v*I
Primary load current is
10000=1.732*230*I
I=25.10 A
Secondary is,
52.48 A
Is This Answer Correct ? | 35 Yes | 15 No |
Answer / k.sri405
10 kva & 20 kva means transformer apparent power that is
combination of active and reactive power so we can load this
transformer below its rating coz load means only active
power .but in case of purely resistive losd we can load this
transformer upto its rating but practically purely resistive
load is not possible.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / kaleem
aroluli which voltage we'll use ? line to line to line to line to ground ?? 230 or 400 this formula to calculate 3 phase current ?? p= 1.73 v i cos@
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / dkverma67
For 3phase transformer
10 KVA=10*1.4 Amp=10.4 Amps maximum
25 KVA=25*1.4 Amp=35.0 Amp max.
Is This Answer Correct ? | 8 Yes | 9 No |
Answer / pillay
the max load you already said as 10 kva and 20 kva. In terms
of kw it will be 10 & 2o kw also, so long it does not exceed
10 & 20 kva ampere ratings.
Is This Answer Correct ? | 5 Yes | 6 No |
why dc series motors never start without some load, and what will happen if starting with out load..
suppose if oil in transformer is not used than what constructional change you will do,for insulation and cooling?
What is the harm if we install primary side 11 KV VCB at a distance of one Km from the 11/3.3KV 12.5 MVA transformer through 11 KV cable.
A group of machines (wind turbines) connected with 33KV feeder and each machines are having individual VCB. The 33KV feeder connected with 110KV/33KV substation. The 33KV feeder tripped by over current at Substation and fault recorded at Substation as OC-R&Y phase. Same time the group of machines VCB tripped by over voltage, the fault recorded voltage was above 66KV by numerical Under/Over voltage relay. While grid drop time, this much of voltage hike is possible?
how is calculated the quantity of weight in hot test xlpe?
Explain with example of functional requirements of protection relay in terms reliability, selectivity, sensitivity
What is the ratio of true power to apparent power in an ac circuit?
in dc series motor if field wdg is shorted then
What is ferro-resonance in electrical system? Why it occurs and what are measures to prevent it?
can induction motor run over the rated speed ?
Ceiling fan motor wiring Hi, I have 2 ceiling fans broken. The receiver/control units burned out due to lightening. One Harbor Breeze and one Hunter's I took them apart (remove receiver units). Now on both of the motor I see 4 wires coming out from each motor I really want to know the function of each wire. Are there anyway I can test to see which is which? After searching forums I know these 4 wires are from 2 sets of coils inside the motor, one is Start winding and the other is Runing winding I could not find the receiver/control unit any where, so I am planing to buy Capacitors and universal remote controls to make the fans run again. Anyone has any idea how to do the wiring, please help Thnks
list the advantages of RCCB over other circuit breakers?