what is the difference between(Flame proof/Explosion proof)&
Fire proof instruments.Both are same or different & if
different in which way because the transmitter which have
approved ATEX flame proof enclouser but it use PTPE O ring
& PTFE Head Gasket,so its (fire safe/fire proof)????????
Answers were Sorted based on User's Feedback
Answer / a.pitchiah
All the answers avoid the direct question. In my opinion
Falme Proof and Explosion Proof mean one and the same,
going through various indirect references.
Fire Proof is different, since the constuction of the items
must be of fireproof materials.Explosionproof or flameproof
need not necessarily be fireproof.
Please comment.
Is This Answer Correct ? | 15 Yes | 2 No |
Answer / swapnilsd
Flame proof or explosion proof intruments are used for
avoiding explosion and avoiding posibilities of short
circuit in highly flamable & explosive area.In this case
flamable media probably being gas,so flamable & explosive
gases catches fire in electric field.
Fire proof instruments are used for protection due to any
type of fire.
So,finally I would say that flame proof/explosion proof
instruments must be fire proof,but out of explosive or
flamable area we can use only fire proof instruments,there
is no need of flameproof instruments.
Is This Answer Correct ? | 6 Yes | 5 No |
Answer / m mouse
Flame Proof or Explosion proof equipment is used in a
Hazardous area where an explosion may occur due to
electrical short circuit or arching of contacts. The idea is
to contain any ignition that may occur inside the
fitting/enclosure such that it does not ignite any gas/dust
or other explosive media outside of the fitting/enclosure in
the general working environment.
Fire proof is just what it says and has nothing to do with
Atex OR Ex equipment, other than the fact that Atex OR Ex
equipment will usually be inherently fire proof because of
their design.
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / swapnil subhash dhamanse
Flame proof or explosion proof intruments are used for
avoiding explosion and avoiding posibilities of short
circuit in highly flamable & explosive area.In this case
flamable media probably being gas,so flamable & explosive
gases catches fire in electric field.
Fire proof instruments are used for protection due to any
type of fire.
So,finally I would say that flame proof/explosion proof
instruments must be fire proof,but out of explosive or
flamable are we can use only fire proof instruments,there
is no need of flameproof instruments.
Is This Answer Correct ? | 4 Yes | 10 No |
I have completed B.E. Instrumentation & control in 2009. i have 3 year industrial job experience in chemical plant.now, I want to join M.E. in external. so, Plese say easiet way and good institute name.
Is SmartPlant Instrumentation taking advantage of the quality assurance procedures within Intergraph?
What is passive connection of instrument in different type of I/O module
I have transmitter of range -20 to -5 kpa.if it is possible to zero trim with atmospheric pressure,means HP and lp having no pressure...what will get after zero trim and it is the right way.....plz give me reply ....
why the steam drum and deaerator level transmitter range is in negative MMWC to zero
3 Answers Emerson, Jindal, JKPM,
What is the difference between floating and fixed voltage?
what is the procedure to isolate flow a transmitter and flushing it?
what is concept of field,control room area in transmitters?
What is the difference bitween control net scaner and device net scaner
What is 3 selection available when configure the burnout protection for controller
0 Answers EI Electrotechnical Institute,
Is there devices to convert mechanical energy/rotational energy into electrical energy.......? PLease suggest me....
What is difference b/w absolute & gauge pressure? EXPLAIN