Extract form appendix K of standard IEC 60947 -2
Voltage
• Ue = Rated operational voltage
• Ui = Rated insulation voltage
• Uimp = Rated impulse withstand voltage
Current
• In = Rated current
• Ith = Conventional free –air thermal current
• Ithe = Conventional enclosed thermal current
Short -Circuit
• Icm = Rated short circuit making capacity
• Icu = Rated ultimate short circuit breaking capacity
• Ics = Rated service short circuit breaking capacity
• Icw = Rated short time withstand current
Trip unit
• Ir = Adjustable overload setting current
• 1.05xIr = Conventional non –tripping current
• 1.30xIr = Conventional tripping current
• Isd = Short time delay tripping setting current
• Ii = Instantaneous tripping setting current

Is This Answer Correct ?    8 Yes 0 No

what is the difference between Ith & Iu rating in MCCB. Particularly on SACE ABB Circuit Break..

Answer / mazed

CCB Ith & Ir Acronym Meaning
05/02/2010 9:16 AM

We are planning to replace our Chiller with bigger capacity.

The motor rating of old chiller is 375 kw whhle the new one
is 570 kw, all at 380 volts, 3phase , 60 hz. The suppllier
required us to a circuit breaker with minimum ampacity of
911 amps.

our existing Circuit Breaker is SACE ABB, Iu =1250, Ue =660
Volts, 3 poles. Their is a rating of Ith @ 45 deg C of 800
Amps maximum and Ir = 6300 max. My questions are:1. What is
the Ith & Ir means. 2. Can i use ourold MCCB with the rating
of 1250 Amps Iu?

Please all extert here help me.

My best regards to all.
Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments
are added.
Join CR4, The Engineer's Place for News and Discussion!
Comments rated to be Good Answers:
These comments received enough positive ratings to make them
"good answers".

* #4 "Re: What is the Ith & Ir at MCCB stand for?" by
JRaef on 05/02/2010 7:01 PM (score 5)

Tornado
Guru
[Tornado's Picture]
Technical Fields - Technical Writing - New Member
Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Ketchikan, AK, USA
Posts: 11914
Good Answers: 421
[Click to collapse or expand]
#1
[Comment] Re: What is the Ith & Ir at MCCB stand for?
05/02/2010 2:42 PM

Ith is the thermal current rating of the breaker. The more
the motor current exceeds this, the quicker the breaker will
trip. I'm unsure of the other abbreviations, but they may
represent the magnetic trip rating, which is nominally
instantaneous.

If the motor requires 911 A, it is likely to trip this
breaker either 1) right away if the starting current exceeds
6300 A, or 2) in a short time if the running current exceeds
800 A. So I don't think this combination will work.
__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Dalton
Associate

Join Date: Nov 2009
Posts: 28
[Click to collapse or expand]
#2
In reply to #1
[Comment] Re: What is the Ith & Ir at MCCB stand for?
05/02/2010 2:59 PM

Thanks, but how about the Iu (1250 Amps) which i believed is
the nominal current rating. Our MCCB rating Iu = 1250 Amps &
Ue is 660 volts. then their is anothr rating which is Ith =
800 max @ 45 Deg C. any idea on this Sir?
Reply
Tornado
Guru
[Tornado's Picture]
Technical Fields - Technical Writing - New Member
Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Ketchikan, AK, USA
Posts: 11914
Good Answers: 421
[Click to collapse or expand]
#3
In reply to #2
[Comment] Re: What is the Ith & Ir at MCCB stand for?
05/02/2010 4:15 PM

My idea on that is exactly as before. If the thermal rating
Ith of 800 A is exceeded by the 911 A motor, the breaker
will trip (sooner or later).

However, if the ambient temperature at the breaker is less
than 45°C, the Ith will be somewhat higher. This may get you
by, but it looks really borderline. Reduced-voltage and
unloaded starting will also help.
__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster
[Click to collapse or expand]
#5
In reply to #2
[Comment] Re: What is the Ith & Ir at MCCB stand for?
05/03/2010 5:16 AM

ASK ABB for their catalogue on MCCBs select yourself you
will find all inputs required you could download the
catalogue from ABB web site.

good luck

murali

Ex power user
Reply
Dalton
Associate

Join Date: Nov 2009
Posts: 28
[Click to collapse or expand]
#6
In reply to #5
[Comment] Re: What is the Ith & Ir at MCCB stand for?
05/03/2010 8:46 AM

thanks. this an old model MCCB from ABB. SACE SN1250 model.
Installed last 1986 by the German Contractors here in KSA.

All I want to know is if could still use this MCCB. But i
think the best solution now is to buy a new MCCB.

Rgards to all.
Reply
[Rated a 'Good Answer' with a score of 5] 5
JRaef
Guru
[JRaef's Picture]
United States - Member - New Member Engineering Fields -
Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door
to God.
Posts: 3209
Good Answers: 419
[Click to collapse or expand]
#4
[Comment] Re: What is the Ith & Ir at MCCB stand for?
05/02/2010 7:01 PM

Extract form appendix K of standard IEC 60947 -2

Voltage

* Ue = Rated operational voltage
* Ui = Rated insulation voltage
* Uimp = Rated impulse withstand voltage

Current

* In = Rated current
* Ith = Conventional free –air thermal current
* Ithe = Conventional enclosed thermal current

Short -Circuit

* Icm = Rated short circuit making capacity
* Icu = Rated ultimate short circuit breaking capacity
* Ics = Rated service short circuit breaking capacity
* Icw = Rated short time withstand current

Trip unit

* Ir = Adjustable overload setting current
* 1.05xIr = Conventional non –tripping current
* 1.30xIr = Conventional tripping current
* Isd = Short time delay tripping setting current
* Ii = Instantaneous tripping setting current

__________________

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

CAn a TJM 10 relay measure over current ?

2 Answers  


why do mostly prefer to generate and distribute electricity in 3 phase..not in 4 phase or 5 phase.??

5 Answers   BSBK, IOCL, NTPC,


how oltc works in rectiformers of higher rating (27 mva,200v dc,120kamps) please provide me full information with diaggram.

0 Answers  


what is the difference between the electrical and electronic choke?

1 Answers  


what type of loads are inductive load & resistive load ?how they different between each other ?

5 Answers  






54 Comments Alok and Bhanu play the following min-max game. Given the expression N = 38 + X*(Y – Z) where X, Y and Z are variables representing single digits (0 to 9), Alok would like to maximize N while Bhanu would like to minimize it. Towards this end, Alok chooses a single digit number and Bhanu substitutes this for a variable of her choice (X, Y or Z). Alok then chooses the next value and Bhanu, the variable to substitute the value. Finally Alok proposes the value for the remaining variable. Assuming both play to their optimal strategies, the value of N at the end of the game would be?

0 Answers   Bajaj, TCS,


What is the difference between Type test and Routine test?

10 Answers  


Difference B/W A/C & D/C Motors..?

10 Answers   Toyota,


Please, if 1kw is equal to 1.25kva; how then do I know how many kva in 7.5kw?

0 Answers  


what is the response time of relays when a FAULT OCCURS IN A POWER SYSTEM?

2 Answers  


what is lrs tank water resistance.

0 Answers  


what is load cell

3 Answers   TATA, Wipro,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)