How do we measure earth fault current in Generator
Transformer(20/420kv),Station Transformer(20/11 kv) and Unit
Transformers(20/11kv) for our plant system, since these
don't have any Neutral earth Fault relay connected to their
Neutral Earth?
But for Unit Service transformers(11/.433 Kv) we have an
Earth Fault Relay connected to its neutral earth.Why is such so?
I assume your generator rating is around 250-315MW.
GENERATOR TRANSFORMER IS YN-d1 or d11, 420kv power
transformer is provided with neutral bushing and solidly
grounded to earth system (U,V,W-N). YOU CAN MEASURE THE
EARTH CURRENT WITH CLAMP ON METER.
GENERATOR 20KV OUTPUT IS CONNECTED WITH lv side of
generator transformer by bus duct. there is a voltage
transformer, 2 winding y/y or three winding VT Y/y-
opendelts. This open delts voltage indicate the fault in
20kv system.
Genrator is provided with 90% and 100 % earth fault
ptortection.
Generator neutral is connected with generator neutral
grounding transformer. Generator neutral transformer
primary is connected to genrator neutral point and other N
is connected to earth. at this point ,You can measure earth
current by clamp on meter.
I assume you have a Generator circuit breaker.
Generator bus is 20kv. This sw.gr feed stn tranformer -
20/11kv system.This station 11kv feed the auxilary
transformers. Vector group of this stn transformer is D/d.
Also unit transformer is 20/11kv. this 11kv bus feed motor
and auxiliayr transformers. vector group is also D/d.
your medium voltage operates as isolated ground system
Unit service transformer is 11/.433 , thereforn vector
group is D/yn. your low voltage feeder need a nuetral.
therefore neutral is brought out. three phase 4 wire, and
230v-n .
please send the rating of transformer. we can explain you
more.
| Is This Answer Correct ? | 0 Yes | 1 No |
what is sevice settings for mccb?How can be it setted?
what is meant by impedence? can you describe easy becuse iam not well familier in electrical?
How to calcluate the current by means wires/cables in square mm
Explain Power factor in simple words
what is mean by current
ELCP USE IN 3 PHASE SUBMERSIBLE PUMP? THEN USE 3 POLE 0R 4 POLE?
what is the diffrence between mcb &elcb?
check list of maintenance of transformer?
11 Answers ABC, Cosmos, EPRON, Essar, Godrej, Hescom, Infosys, KPTCL, TCS,
what you mean by vector group of a 3 ph transformer
What is the use of lag compensator?
how to find three phase complex power in per unit and MVA?
briefly explain principle of resistance welding
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)