How do we measure earth fault current in Generator
Transformer(20/420kv),Station Transformer(20/11 kv) and Unit
Transformers(20/11kv) for our plant system, since these
don't have any Neutral earth Fault relay connected to their
Neutral Earth?
But for Unit Service transformers(11/.433 Kv) we have an
Earth Fault Relay connected to its neutral earth.Why is such so?
I assume your generator rating is around 250-315MW.
GENERATOR TRANSFORMER IS YN-d1 or d11, 420kv power
transformer is provided with neutral bushing and solidly
grounded to earth system (U,V,W-N). YOU CAN MEASURE THE
EARTH CURRENT WITH CLAMP ON METER.
GENERATOR 20KV OUTPUT IS CONNECTED WITH lv side of
generator transformer by bus duct. there is a voltage
transformer, 2 winding y/y or three winding VT Y/y-
opendelts. This open delts voltage indicate the fault in
20kv system.
Genrator is provided with 90% and 100 % earth fault
ptortection.
Generator neutral is connected with generator neutral
grounding transformer. Generator neutral transformer
primary is connected to genrator neutral point and other N
is connected to earth. at this point ,You can measure earth
current by clamp on meter.
I assume you have a Generator circuit breaker.
Generator bus is 20kv. This sw.gr feed stn tranformer -
20/11kv system.This station 11kv feed the auxilary
transformers. Vector group of this stn transformer is D/d.
Also unit transformer is 20/11kv. this 11kv bus feed motor
and auxiliayr transformers. vector group is also D/d.
your medium voltage operates as isolated ground system
Unit service transformer is 11/.433 , thereforn vector
group is D/yn. your low voltage feeder need a nuetral.
therefore neutral is brought out. three phase 4 wire, and
230v-n .
please send the rating of transformer. we can explain you
more.
Is This Answer Correct ? | 0 Yes | 1 No |
why do we prefer -48 volt instead of -24volt or -12 volt etc. ??
WHAT IS THE MEANING OF CYWY
A low wet bulb temperature indicates
sir my exam is on 19/6/2013 under electrical branch pls send me sample aptitude questions as well as sample technical questions for jindal steel and power company
Earth Is a very good conductor or very good insulator.? If a good conductor then why current donot flow through small piece f earth and if a good insulator then why we use it as return path in lines.???
how to select DG set for certain load?
In transformer which temp should be less oil temp are winding temp?
how to find out difference between ELCB, MCB and RCB on looking on it
What is GIS (Gas Insulated Switchgear)
how to identify the failer of igbt
transmission line losses
If the primary side current of 33/11 transformer is 64 amps then what will be secondary side current?