What is the clear distance between a MV panel(rear side) and wall.
Answers were Sorted based on User's Feedback
Answer / annonymous
it should be such that a person can easily work there and depend on the width of the rear access door for the switchgear which shall be opened before accessing the rear of the panel.
Rear access is mainly required for the cable terminations.
we keep it usually 800mm to 1000mm.
| Is This Answer Correct ? | 7 Yes | 0 No |
refer to IEC about AFLR, it require 900mm minimal for rear side clearance and 1300mm for front panel clearance, and 600mm for ceiling
| Is This Answer Correct ? | 0 Yes | 0 No |
What is PLL? what are it's advantages?
why battery dc voltage become Half when we check with respect to ground for example 120volts + and - terminals and when we check + terminal with Earth thats 60volts why 60volts same result on 24Volts and with ground 12Volts only expert answer that thanks we can not ground the battery.
I have suguna 3 hp pump for my agreeculture work.It deliver the water from 45 feet well .I suffered by powercut.During powercut i got 2phase supply only .My question is can i run the pump in 2 phase supply using capacitor?.Can u explain me how to connect the capacitors?
In an ACB shunt trip coil and undervoltage coil operated normally( breaker open and charged). But closing coil not operating untill manually discharge and recharging. Any help.
why high current produce in case of transformer when turns are internally gets shorted.
Whis machine is having higher efficiency Transformer or Generator
Why you are switching off arc protection mcb when you are taking shutdown for lv board.
we have 3 phase 4 wire supply 230/415 V.AC and our distribution is single phase or we have all single phase 220 v,ac operated appliances. and noted the current with help of clamp meter Red to N = 20 Amps. Yellow to N = 45Amps and Blue to N = 30 Amps ( total is 95 Amps ) what will be neutral current on the main .
what are the deffects for failure of PLC?
Does the ELCB or RCCB trip when it is connected to a primary side of a welding transformer?
when we r using 3.5 cable for a bldg. and put laod on each phase using the neutral and neutral is the return paht for the phase so the current of the neutral must be Ir+Ib+iY (return).But the size of the netural is .5 as comper to the phase.
What is the size of a 60 watt and 80 watt tubelight?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)