what to do with nuetral when Generators are running in
parrellel

Answers were Sorted based on User's Feedback



what to do with nuetral when Generators are running in parrellel..

Answer / guest

First generator need to connect ,while second generator
nuetral kept open

Is This Answer Correct ?    14 Yes 2 No

what to do with nuetral when Generators are running in parrellel..

Answer / rajesh anne

any one of the generator neutral need to be grounded.if it
is multiple generators also one generator neutal must need
to be grounded because the unbalnce currents will pass
through the neutral while it was running in parallel.

Is This Answer Correct ?    8 Yes 1 No

what to do with nuetral when Generators are running in parrellel..

Answer / amrinder

please give clear answer.....waiting..

Is This Answer Correct ?    5 Yes 2 No

what to do with nuetral when Generators are running in parrellel..

Answer / muninanjappa

First Generator must be grounded and next generator neutral
must be left open works as floating neutral.
Both Alternator neutrals should not be earthed while running
in parallel

Is This Answer Correct ?    4 Yes 1 No

what to do with nuetral when Generators are running in parrellel..

Answer / b madhu sudhan reddy

when two genarators are conected in parllel then it must
satisfy the synchronisam i.e it must satisfys certain
conditions.suppose when it falls to out of synchronisam
then there is chance of occuring the fault i.e there is a
chance for circulating high currents,at that particular
situtation the nutral will help for flowing that currents
to ground&it also protect the system when the lightning is
occur

Is This Answer Correct ?    4 Yes 2 No

what to do with nuetral when Generators are running in parrellel..

Answer / guest

the neutral is grounded

Is This Answer Correct ?    1 Yes 0 No

what to do with nuetral when Generators are running in parrellel..

Answer / guest

earth

Is This Answer Correct ?    1 Yes 1 No

what to do with nuetral when Generators are running in parrellel..

Answer / sreeraj n

the generator ,which we first connect to bus ,that generator nuetral need to connect to load ,other generators nuetral kept open

Is This Answer Correct ?    0 Yes 0 No

what to do with nuetral when Generators are running in parrellel..

Answer / mallikarjuna reddy

I Hope we have to connect the both neutrals(individual
alternators)to the earth.if fault occurs when that
synchronism fails unbalance currents will flow through this
neutarl to ground.

Is This Answer Correct ?    1 Yes 2 No

what to do with nuetral when Generators are running in parrellel..

Answer / b.ramesh babu

when the generator satisfing the parallesm conditions then
the neutral is grounded because when when the parellelism
conds are not satisfied then the circulating currents are
generated which become one become motor and other become
generator..........so d circulatind currents are flow to
the grounded..

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

What is the difference between MCCB,ELCB,RCB & MCB

2 Answers   Bhel, HCL, HPL,


why we are using star connection and delta connection? difference?

5 Answers  


What are the condition for parallel operation of transformers?

2 Answers   Alfanar,


why we are using the 2 slope in differential relay?but in busbar differential we are using only one slope. what is the reason.

1 Answers  


why we use MV panels??? what's r all the needs

4 Answers  






tell me about roaster switch .& what is the function in transmission & distribution?

0 Answers  


i have install 750 kva distribution transformer at my site and want to do neutral earthing. what calculations should i follow to determine earthing conductor material and size?

0 Answers   MTDC,


different types of electrical cable?

1 Answers   Green Power,


What is voltage in two phase?

7 Answers   ABB, SSG,


What will happen if an AC induction motor is applied with DC voltage?????????Kindly give all the posssible answers...

2 Answers  


We have ONLINE UPS 15KvA (3PHASE 440V I/P,3PHASE O/P,440V) I want to step down from 440 to 220 V What to do. Pl. suggest with specification.

1 Answers   ARDE,


1. What is the difference between ac induction motor and ac synchronous motor?

11 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)