Answer / guest
First generator need to connect ,while second generator
nuetral kept open
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / rajesh anne
any one of the generator neutral need to be grounded.if it
is multiple generators also one generator neutal must need
to be grounded because the unbalnce currents will pass
through the neutral while it was running in parallel.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / muninanjappa
First Generator must be grounded and next generator neutral
must be left open works as floating neutral.
Both Alternator neutrals should not be earthed while running
in parallel
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / b madhu sudhan reddy
when two genarators are conected in parllel then it must
satisfy the synchronisam i.e it must satisfys certain
conditions.suppose when it falls to out of synchronisam
then there is chance of occuring the fault i.e there is a
chance for circulating high currents,at that particular
situtation the nutral will help for flowing that currents
to ground&it also protect the system when the lightning is
occur
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / sreeraj n
the generator ,which we first connect to bus ,that generator nuetral need to connect to load ,other generators nuetral kept open
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mallikarjuna reddy
I Hope we have to connect the both neutrals(individual
alternators)to the earth.if fault occurs when that
synchronism fails unbalance currents will flow through this
neutarl to ground.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / b.ramesh babu
when the generator satisfing the parallesm conditions then
the neutral is grounded because when when the parellelism
conds are not satisfied then the circulating currents are
generated which become one become motor and other become
generator..........so d circulatind currents are flow to
the grounded..
| Is This Answer Correct ? | 0 Yes | 2 No |
why genarator genarating voltage 11 KV?
Sir 33kva 2 transformer load 900 amp calc 1800 amp mana jayega
In a closed circuit if two 5volt power supplier are connected in parrel what is the current direction in tihs circuit?
how can we connect the capacitor bank to improve the power factor?
why the pf of semiconductor device is improved the electrical devices
How do i perform grounding of star point of Genset (400V) for making connection with step up transformer of DELTA-DELTA (400V to 20KV) ? while Genset itself has its own neutral and grounding bus bar inside genset breaker box whereas we have another neutral and grounding busbar in synchronizing panel next to genset at maximum distance of 6meter, would someone pls advice if we can only perform neutral grounding in synchronizing panel or should we ground neutral on both places inside genset breaker box and synchronizing panel.
How to protect sensitive loads such as Dosing pumps inside a factory from voltage surge/voltage fluctuation.
EXPLAIN THE WORKING OF SERIES REACTOR IN HT CAPACITOR BANKS (FOR VOLTAGES & CURRENTS)
what is difference b/w earth and ground?
Advantages/Disadvantages of earthing of neutral bus on MSB instead of separate neutral earthing for transformer/DG sets feeding to MSB
In siemens PLC, why do we want to move the data ?
How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)