what is GRR(Grid Rotot resistance)?Why it is used beside of
LRS?
Answers were Sorted based on User's Feedback
Answer / surya prakash
GRR(Grid Rotot resistance) is a resistance box which is
used for speed control of slipring Induction motor & save
the power.The Induction motor having high starting torque
needs resistance in rotor circuit by the use of GRR we can
add the resistance in the circuit & increase the slip so
torque, ones motor will start we reduce the resistance of
GRR by Contactor,and at full speed shott all resistance.
LRS is used where no speed control is required only high
starting torque is required.
Is This Answer Correct ? | 123 Yes | 16 No |
Answer / rupesh usadadiya
GRS= Grid resistance STARTER
GRR= Grid resistance REGULATOR
While:LRS = Liquid Resistance STARTER
& LRR = Liquid Resistance REGULATOR
Both GRR & LRR or GRS & GRS are technically similar.
In both the equipment we are adding the resistance in the
rotor circuit.
BUT THE MAJOR DIFFERENCES ARE:
GRR a solid form of resistance, While LRR is Liquid form of
Resistance.
In GRR onece you define the resistance value, we can not
change the resistance value without changing the hardware.
While in LRR we can change the resistance value by changing
the Liquid concentration(PH).
In Regulators, the resistance is continue in circuit, hence
the temperature of resistance increase.
In solid resistance its possible to withstand the high
temperature without major changes in resitance value, while
in Liquid Resistance if temp. goes above 90 degree C, the
resistance value is change drastically.
Hence the Grid(Solid) resistance mainly used in speed
regulators.
If we want to use the Liquid Resistance as a controller,
then we need to add a heat exchange or cooling system to
maintain the Liquid temperature.
Any one can find out the more details on GRS/GRR and LRS/LRR
on www.resistancestarter.com or www.pew-india.in
Is This Answer Correct ? | 42 Yes | 4 No |
Answer / sayan
It is not always true that Liquid Resistance Starter cannot
be used as spped control device. In fact it provides a
smoother speed control of induction motor that GRR as the
later is having stepped speed control.
Is This Answer Correct ? | 45 Yes | 13 No |
Answer / rajesh ku sahu
GRR(Grid Rotot resistance) is a resistance box which is
used for speed control of slipring Induction motor & save
the power.The Induction motor having high starting torque
needs resistance in rotor circuit by the use of GRR we can
add the resistance in the circuit & increase the slip so
torque, ones motor will start we reduce the resistance of
GRR by Contactor,and at full speed shott all resistance.
LRS is used where no speed control is required only high
starting torque is required.
Is This Answer Correct ? | 29 Yes | 6 No |
Answer / mohan
LRS GENERALLY USED FOR STARTING OF MOTOR AND REDUSE THE
STARTING CURRENT AND INCRESE THE TORQUE.GRR ALSO SAME USES
& SPEED CONTROL BY VARRING THE ROTORRESISTANCE OF MOTOR.GRR
IS AGRID RESISTANCE BOX IS CONNECTED WITH ROTOR IN
SERIES.GENERALLY THIS CONTROL USED IN Y/Y CONNECTION WOUND
ROTOR MOTORS
Is This Answer Correct ? | 23 Yes | 6 No |
Answer / sanjay
GRR USED FOR HIGH STARTING TORQUE AND LIMIT THE STARTING
CURRENT.
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / arun kumar.k
GRR it is may be resistance box it is the speed controlable
device and power saving device it is slip ring induction
motor Or rotor resistance motor
When Resistance Decereases speed increases
when resistance increases speed Decereases
Is This Answer Correct ? | 7 Yes | 5 No |
Answer / ashish chouksey
GRR is a grid resistance box in which the resistance is
controlled by contactor logic as per slip ring motor
requirement and the purpose of grr is to control the speed
of motor by change the resistance of rotor circuit and save
power.LRS(Liquid rotor starter)is used for starting of slip
ring induction motor only . in lrs we use water with soda
for add the resistance and the ph value should be 9-11
Is This Answer Correct ? | 6 Yes | 5 No |
Answer / manoj verma
Grr stating toruc. Bhut and rissitens for contoral . Anf seving off power
Is This Answer Correct ? | 3 Yes | 9 No |
Advantages/Disadvantages of earthing of neutral bus on MSB instead of separate neutral earthing for transformer/DG sets feeding to MSB
suppose there is afault in transmission line connected to a generating station, then what r the adjustments u will take to without loss of synchronism?????
how to select the surge suppresor for the 33 KV supply and what will be the rating, selection guide
can any one explain about when EB supply failed then how the load will transfer onto DG's step by step.
Waht are the protection should be use in HT/ LT side of the same Xformer?
How will A Medium voltage circuit breaker(11 kV voltage level) operate under short circuit fault condition whether It is having short circuit release like Low voltage circuit breaker or relay should be given?
Why in KVA diesel engine? Why not KW
how the global warming take place?
how wecalculate breaking capcity of acb mcb mccb .explain with example
11 kg trivevter meter has rating of -/5amps. And pt ratio11000/110v and is connected with 11kv ct/pt unit of cr ratio 75/5amps. And pt ratio of 11000/110v while checking accuracy of meter with HT Accuchek meter what value of PT ratio and CT ratio to be filled in Accuchek meter
What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer?
what is the necessity of neutral in 3 phase system?