what is the main function of lbb
protection
Answers were Sorted based on User's Feedback
Answer / vishreddy205
for the protection of breaker when
breaker doesn't operate for
abnormalities then main breaker act
as a backup protection
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / hardip dodiya
For Protection of Breaker and protection of EHV Bus-bar in
EHV and HV switchyard. all S/s breaker have one NO/NC
Contact connected to Bus-bar control panel in which. at
time of fault, Breaker Stuck up due to Mechanisam prob or
failure of Trip coil or any mechanical damage problem.
After it TIME-Delay time almost 200ms. busbar control
panels sense this abnormality and give command to all
breaker to trip which is connceted to EHV Bus-bar.
Protect the S/s Equipment.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shailesh
The main function of LBB to get protection (To trip breaker)
when main breaker not trip due any reasons.
| Is This Answer Correct ? | 1 Yes | 1 No |
.if the vector group of two transformers is not same n tey r connected in parallel operation then what will happen?
Differenciate between circuit wiring and sub main wiring with illustrations
What should be the earth pit resistance value?
We have 3 Gensets 1.500kva,2.380kva,3.250kva How can we connect in common busbar&we have variable load.
In transmission line the line power loss only accured at resistance the inductance and capacitance wont consume power is it correct?
how the arcing is made in ac electric arc furnace? ( between the three electrodes in any sequences or between the electrode & the charge(steel))
As Electricity Generates in MW I w'd like to know What are the factors we have to consider regarding the transmission of electricity from generation station to Public uses(230 V)
how many by pass system in online UPS.
Please explain me about Relay curves and their sources to read ?
In Energy meter How many rotation Equal to one unit.
for ac networks if the voltage wave form is V=Vm sinwt here the voltage Vm=230 for the frequency 50hz then the time period is 0.02 sec then for the time period 0.12 sec what is the voltage
Why CT secondary is grounded?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)