Why is starter necessary for a three-phase induction motor?

Answers were Sorted based on User's Feedback



Why is starter necessary for a three-phase induction motor?..

Answer / farha

A starter is needed for a three phase induction motor
because at the time of starting, if induction motor is
started directly, it will draw large amount of current
which causes damage to adjoining equipments.
Thus, a starter is needed in order to limit the starting
current.After the motor has started at reduced starting
current and hence reduced voltage, the connections are
diverted towards the mains supply so that now, the motor
can run at higher starting current and voltage.
Four types of starting methods are employed:
1.Star-Delta
2.Auto transformer method
3.Primary resistor starting.
4.Direct On-line.
Low rating upto 7 H.P motors can be started directly.

Is This Answer Correct ?    607 Yes 51 No

Why is starter necessary for a three-phase induction motor?..

Answer / jessy

By starting an induction motor with starter limits the
starting current and starting torque .


Note - Upto 5 to 7.5 HP Three phase induction motors
generally started direct on line .

Is This Answer Correct ?    235 Yes 51 No

Why is starter necessary for a three-phase induction motor?..

Answer / saurabh

at the time of starting slip S= 1, so the rotor resistance
which depends on slip i.e.
R2(1-S)/S will be equzl to "0",
i.e. rotor will act as short circuit.
hence initailly motor will draw heavy amount of current.
So in order to reduce this inrush current(5 to 7 times of
rated current), we apply less input voltage at the time of
starting so that input curent will be low(as in case of
star connection) & after some time or specified time input
will be fed in Delta connection.

if u understand this then ok other wise read more books in
details...

Is This Answer Correct ?    164 Yes 24 No

Why is starter necessary for a three-phase induction motor?..

Answer / msimanmg

The starters are used to limit the starting current to
accepteble value.

Is This Answer Correct ?    114 Yes 17 No

Why is starter necessary for a three-phase induction motor?..

Answer / g.v.suresh kumar

AT THE STARTING OF THREE PHASE INDUCTION MOTOR THE STARTING
CURRENT IS HIGH IT IS DUE TO AT THE STARTING THE BACKEMF IS
0.SO BY USING STARTER WE CAN LIMIT THE STARTING CURRENT

Is This Answer Correct ?    146 Yes 57 No

Why is starter necessary for a three-phase induction motor?..

Answer / abanikanta

Starter is used to reduce starting current.starting current
is usually large because of inertia,charecteristics of
motor winding(at starting slip=1,rotor resistance low
implies less back emf).So at starting we use starter .for
example.STAR DELTA starter.by using a starter at least the
switching is improved which is much important for safe and
longer life time use.simply a DOL can be used for lower
rated motors (up to 07 HP)in this case.for higher rated
motors (up to 15 HP)we can use a star delta connection.a
delta connected motor takes 1.7 times line current than a
star connectd motor.think ! at starting the current is
almost halved .Now a days we use drives (power electronics
products which not only takes care of starting of a motor
(improving power factor) also controls it as perrequirement.

Is This Answer Correct ?    56 Yes 8 No

Why is starter necessary for a three-phase induction motor?..

Answer / patanjali

1--it limit the starting current.
2--increase the starting torque.

Is This Answer Correct ?    75 Yes 32 No

Why is starter necessary for a three-phase induction motor?..

Answer / bhavik parekh

starter is reqired for the purpose of reduce starting
current. starting current reduce in starting period so that
starting torque is increase. another thing is that if
starter is not provided than high amont of current flow in
starting beacuase of that it may be chances to damege
itself and alose its adjoining m/c.

Is This Answer Correct ?    41 Yes 18 No

Why is starter necessary for a three-phase induction motor?..

Answer / balasivakami

starter is required to limit the high starting current

Is This Answer Correct ?    32 Yes 10 No

Why is starter necessary for a three-phase induction motor?..

Answer / monika khatri

when the induction motor starts.slip i.e "s" has a value
1...and hence the internal resistance value becomes
0..since resistance is directly proportinal to (s-1)....as
the resistance becomes 0..according to ohms law current
becomes very high.....tha value of current is about 5 to 6
times the full load curent......therefore the motor must
accelerate to high speed ,,which is not possible at "load"
condition.....and hence the motor may burst due to
overheating.............to prevent the motor from bursting
by reducing the value of current we use a STARTER....

Is This Answer Correct ?    24 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

Why electrical engineer use Cu Strip for transformer neutral why not GI Strip? What if we use GI instead of Cu does it affects the transformer performance.

7 Answers  


Why magnetic flux produces an induced current?? what is the detailed procedure ?? ans plz

1 Answers  


in india ac frequency is 50hz, but in foreign countries it is 60hz,whwt is the reason

9 Answers   SVIT,


If connected load of Asphalt plant is 375Kw. What suitable KVA DG set is required. What is calculation formula. what extra load have to consider. in what efficiency it will work.

8 Answers   MAHINDRA,


why induction motor takes high current?

1 Answers   Emerson,






Will u plz give me simple diagram for tube light connection & also function of chock?

8 Answers   Bhushan Power Steel, Dalmia Group, Jindal, Practical Viva Questions, TCS, Windmoller,


what is relation between vector group of transformer and its load hormonics?

1 Answers   Sanmar,


What will happen to the speed of synchronous machine subjected beyond the pull out torque? Are the behavior shown by rotor remains same for both the alternator and motor?

1 Answers  


why ct's&pt'S out put called as burden,why compelsary short ckt the secondary of ct's while removing the burden?

0 Answers  


What is signal flow graph?

0 Answers  


What is the tube exial fan?

0 Answers  


what is differnt between metering CTs an protection CTs

10 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)