why we use star connection in HT motor? and delta connection
in LT motor
Answers were Sorted based on User's Feedback
Answer / vinoth
In HT motors it will reduce the starting current up to 60 percent thats why we prefer star to delta conection..........but in LT motors we use Direct online starter/.......it doesnt reduce the starting current
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / madhu
The starting current for motors is 6 to 7 times full load current. So start-up power will be large if HT motors are delta connected. It may cause instability (voltage dip) in case small Power system. In starred HT motor starting current will be less compared to delta connected motor. So starting power is reduced. Starting torque will also be reduced. (It will not be a problem as motors are of high capacity.)
| Is This Answer Correct ? | 0 Yes | 0 No |
how dia of wire and angles are calculated for overhead shielding wire to protect substation equipment from lightening strokes???
What kind of Neutral CT can be placed in 11/0.433KV transformer to be used and what are its specification?
why characteristics of overcurrent relay is time-->psm instead of time-->current?
is the electrical energy photo copy possible or not???????????? give me some idea about that i m very great full tu u.
why when i start my diesel generator it takes 1 minute or less then stop, and i checked the oil sensor is ok and when the generator start i can get 220 voltage but it it is stop after 1 minute or less, how can i solve this problem?
Sir, My doubt on cable sizing calculation, Load:74 KW calculated cable 1 run 50mm2. Now client asking us to reduce cable size by increasing runs. Sir, My question now when my mind strikes with 2 options 1) Divide load 74/2 = 36 and calculate cable for 36+36 making it 2 runs or 2) Simply i can divide 50mm2 /2 ie. 2 runs of 25mm2 Please suggest me sir
Dear Sir, we met a disaster with our 62.5 kva genset, after rewinding we informed by our contract engg that due to return current coming in neutral & impropper earthing this happend. But after all set up & load balance we checked & found again we have about 20 to 32 amp return current on neutral. we have 12 airconditioner + 12 mini fridge on single phase line. Pl suggest any idea to solved this problem
what is mean by derating factor?
why inductancce of armature inductance of dc machines is neglected?
Why is it not possible to operate a star-delta transformer in parallel with delta-delta transformer?
What is the power factor of an alternator at no load?
Which is stiffer between salient pole rotor and cylindrical rotor synchronous machines? Justify your answer.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)