Answer / touch2gobi
Derating Factor value depends upon the motor environment,
For example:
Motor design temp – 45 deg C
But motor location ambient temp 65 deg C (near any burner
or heat source)
So motor performance (rated power) will reduced due to
ambient temp.
For that motor manufacturer given Derating Factor value.
Ex:
Rated power = 45 kW
Derated power = 42 kW (Operating Temp – 50 deg C)
| Is This Answer Correct ? | 25 Yes | 19 No |
Specify for Cables - Flame Retardant and Fire Resistant?
Explain Gas Turbine startup and shutdown sequences
wht is dcs architecture ? can u give example?
what is controlling card in dcs? how u measure dcs memory?what is bus in dcs?how u know dcs speed n ehternet speed?
types of transformer.. 1ph 3ph or core shell?
typical loop drawing of a simple feedback control comprising of one transmitter and one control
whats the problem will arrise if we rotate the hosing screw of the differential pressure transmitter?
can we use flow transmitter instead of level transmitter?
what is the deference bitween DCS and PLC SCADA HMI System for Power Process Industry.
difference between DCS @ SCADA system? and how can use in field
if the neutral and ground of ups voltege are connected together in the source itslef then why the voltege b/w neutral and ground comes positive in some other destination inspite of having earth pit. how can we mimmise this?
Which standard of hazardous area classification used in India?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)