Answer / manuks
I assume that the machine we talk about is synchronized
with some power grid. In this case the machine will run at
the frequency of this grid. Any fluctuation on the part of
this machine will bring the synchronizing torque into play
and pull the machine back to synchronous speed. Now suppose
we are opening the governor valve to increase the machine
speed. The synchronous torque will immediately put more load
on the generator, to prevent it from speeding away. This
will result in an increase in its load. Any effort to
decrease the speed will result in the synch. torque removing
some load from the machine and again its speed wil remain
the same.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / arvind
first we will know why governor is used in power plant is
because to maintain frequency constant, in india it is 50hz
now by opening the turbine governor valve increase the
generator load because as you load increases, the frequency
will drop and it is the most impontant thing to maitain
frequency thats why it is done.
| Is This Answer Correct ? | 8 Yes | 5 No |
Answer / mitesh
governor valve increase it that time generator load is
deincrease
| Is This Answer Correct ? | 3 Yes | 7 No |
The following equipment are installed ia a plant 1. 110KW Induction motor 4 Nos 2. 30 HP motor 3 Nos 3 15 HP Motor 3 Nos 4 7.5 HP motor 4 Nos what is total load of plant if one of each is stand by.
What happens if you give supply to the rotor of three phase induction motor?
What is kirchoff ’s current law (kcl)?
what shall be no load voltage of 132/33 kV transformer ? is it 33 kv of 34.5 kV
In which iron losses is higher induction motor /transformer
which MPU register provides the address from which the next instruction byte is to be fetch?
how much value of resistance should connect to 15 kw, 6 pole 3 phase slip ring induction motor having RV-240, RA-42.
What is difference between PLC and SCADA
13 Answers Uflex, Vimal Fire Controls,
how can we find thae value of capacitor for single phase motor. what is difference between starting capacitor and running capacitor.
WHY THE TRANSFORMER VALUE MEASURES IN KVA INSTEAD OF KW.
Difference between online and offline UPS?
how can calculate resistance box for 15 kw, 6 pole, RV-230, RA-42 motor
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)