Why Neutral Earthing pits and body earthing is
interconnected
Answers were Sorted based on User's Feedback
Answer / kaustav bhadury
Body earth pits and Neutral earth pits must never be
interconnected.
As per Indian Standards, they must be seperately grounded
into different Earth pits.
Is This Answer Correct ? | 15 Yes | 2 No |
Answer / dayal varma
to make standby if neutral fail then the device get the
neutral from the earthing.
Is This Answer Correct ? | 10 Yes | 10 No |
Answer / yogesh
If neutral earthing pit is separate & body earthing is
separate & if there is body earth fault voltage will develop
at the body suppose 230 V & someone touches body & neutral
potential difference will be 230 V & person will get shock.
If both pits are interconnected same potential will be there
& PD will be zero. So no shock.
Is This Answer Correct ? | 2 Yes | 6 No |
Upload data by LSMW via BAPI in SAP system.
I want to wire sizing calculator which website is available it
How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?
For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply was applied at the HV. Connection between Aa was made with a 2.5mm cable. As soon as power was switched on the cable caught fire and burnt. This test was then abandoned. It is noteworthy to say that a similar cable was also used in a similar transformer for the same. The cable did not burn and test was successfully completed with good result. What is wrong? Please, help me out.
Formulae for calculating the transmission line losses for different voltage levels
what is the acb tripping & closing voltage.
Why delta star trformers are used for lighting loads?
Is a contactor (or master relay) required between incoming lines and a VFD? The question goes to safety. If a contactor were used before the VFD and an e-stop engaged then the motor will coast to a stop (i.e. VFD loses power) instead of stopping much faster if the VFD braking fucntion were used. It would make more sense to keep power on the VFD.
what is difference between short ckt and overload?
How to calculate the current rating of power cables ?
what is the effect if we add capacitor on DG supply, it has any loss or benefit.
What is Neutral Transformer? what is the use of this?