ON RADAR INTERFACE LEVEL TRANSMITTER IF DI-ELECRIC IS WRONG
WITH CONTINIUS PROCESS THAN HOW CAN INDENTIFY OR HOW CAN I
PUT NEW DI-ELECTRIC VALUE?(ROSEMOUNT-TDR-3300-COXIAL PROBE
TYPE)
You said interface level so I must assume you are measuring
oil and water. My experience is on the Khrone BM100 A but
your radar might be similar since the both use TDR technology.
The dielectric constant of crude is about 2 to 4 and water
is 80. The variance in dielectric constant will have a small
effect, so in order to find the right valve one quick way is
to use your sight glass to set the dielectric constants so
that the radar reads the same as the sight glass on the
water and oil. a Good average is normally 2,5 and 80.
Unfortunately this will not work unless you have setup your
Z/S parameters correctly.
If you are still having problems you need to do a complete
setup from scratch. In order to do this you need to get hold
of the design engineer's internal vessel drawings and look
what the calibrated span should be. What you are interested
in is the exact mm measurements from vessel bottom to Z/S
points or positions. From there it is just a matter of
taking exact measurements in the field of your vessel and
your radar installation and make yourself a neat, accurate
detailed drawing to indicate the design spec positions and
the actual position of your probe in relation to the vessel,
and put these measured values in the output 1 and output 2
parameters, keeping in mind zero position is measured from
the probe bottom up and 100% is also from the probe bottom
up and not from zero position up. So if you can see where
the design engineer have said zero should be and you can see
in exactly what position your probe is in relation to those
points it is a matter of calculating how high you need to
measure up from probe bottom to get to those Z/S points
marked by the design engineer. It takes a bit of
trigonometry to do but is easy enough.
Typically these parameters should look something similar to
this. Output 1 (Top product level) 4mA = 150mm, 20mA =
2500mm, Output 2 (Bottom product) 4mA = 150mm, 20mA = 2500mm.
Look strange I know but we have found it is better to set
them both the same instead of trying to set each one to it's
individual span. Both Spans are setup in reference to actual
vessel level %. Interface is also a actual level measurment
in relation to the whole vessel and not to just half the
vessel where for instance to where your wier plate is. If
you do this it will have the effect that you have a very
sensitive interface measurement to a slow level measurment
making your control very difficult. We have done it at one
point and it worked eventually, but it was very difficult to
optimize and get stable control, and even the smallest upset
will cause everything to go crazy again.
In this example the 150mm might be the mm you need to
measure from the probe bottom up to get to the Zero position
of the actual vessel as indicated by the design drawing and
the same with the 2500mm. Obviously just examples. This is
where your exact measurements in the field comes in.
NB!!
Also make sure you have the right probe length in the "tank
Height" parameter and not the real vessel height.
This probe length is normally stamped on the little spec
plate on the head by the supplier.
Good luck!
Is This Answer Correct ? | 7 Yes | 0 No |
Specify eight technical requirements that you would consider important, when deciding upon a particular control valve?
Im working in a shopping center, it is also hotel and office building, two towers exactly and someone is proposing a PLC control for the HVAC system, but Im thinking of a DDC control system. in this case what is the difference between PLC and DDC control?
What is the meaning of slope in PH transmeter?
Can we use thermocouple in generator of power station replace RTD(pt 100)? if we don't have any place for use RTD.
How can corrosion alter the accuracy and precision of a C- Bourdon tube pressure gauge?
EXPLAIN PROPOTIONAL INTEGRAL DERIVATIVE CONTROL ACTION?
hi vishok this is noor plz tell me what type problems will occured i use T/C in the place of RTD in (FEED WATER TANK),plz send ur e-mail address to my ID (mail2noor.hyd@gmail.com)
generally for transmitter we are giving supply 24vlts?but we are getting output 4-20ma ? how it is possible? is there any operation inside the tx?pls give complete information?
i want all model questions paper for robert bosch
what are the steps I have to deal with?
can i use capillary type dp transmitter converted to capillary type pressure transmitter. if i removed one side capillary tube its work correctly?
model question paper of instrumentation for Jindal GET 2010.plz reply sudhanshukumar08@yahoo.com