Answer / naveen
Logically Zero milli amps means no current in the circuit .
if we have an initial value to be measured , we cant measure
it as zero milli amps . It means no current in the circuit
or the circuit is open . so we go for the span of 4 to 20 mA
. this is coz we can easily split 4- 20 as multiples of four
(4,8,12,16) which means 0%,25%,50%,75%and 100% respectively.
| Is This Answer Correct ? | 24 Yes | 4 No |
Answer / sanjay sojitra
The live-zero represented by 4 mA allows the receiving
instrument to detect some failures of the loop, and also
allows transmitter devices to be powered by the same
current loop (called two-wire transmitters)
| Is This Answer Correct ? | 15 Yes | 2 No |
Answer / nirmalya basu
In both of the measurement 20ma represents full data and 4ma
or 0ma shows no data.But with 0ma we cant diagnose the wire
breakage in the transmission line but with 4ma we can diagnose
because if this type of fault is occurred then it shows
0ma.Thats why 4 20ma is used.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / vikash tiwari
4-20ma is a linear system.
Live zero system used in loop so 4-20ma use.
Various instrument use in a loop,when one instrument is faulty so not required to check all loop instrument in live zero system.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is DeltaV?
Why we use DPT? can we use PT instead of DPT?
what's meanning of 1250KVA and how to calculate with Volttage and Current. answer give with example.
plz... clarify my answer, how to calibrate vaccum (DP)leveltransmitter,it is hart. (digital).DETAILS:(coloumn)closedtank height 2650mm,and tx range is 0-1500mmH20.
please explain about actuator action? direct action & return action ?
What is the difference between ff transmitter and non ff transmitter
can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0 to 10 Kg/cm2 ?.. Will it affect 4 to 20 mA output signal which we will feed to the PLC.
I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happened???
how we can calibrate an Interface level transmitter online
What is surge and how is it prevented, what is the purpose of bypass valve across AS valve.
What is Erosion in a control valve?
Conversions
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)