How much KVAr bank reqired for 630 KVA transformer on full
load for maintain power factor upto.99

Answers were Sorted based on User's Feedback



How much KVAr bank reqired for 630 KVA transformer on full load for maintain power factor upto.99..

Answer / dhanesh koshti

Capacitor calculation is depends on load. if 630 KVA transformer is loaded fully with load p.f.=1 then no compansation is required but if the same is fully loaded with load p.f. = 0.8 then, kvar required is calculated as below:
KVAR = KW ( tanǾ1-tanǾ2); Ǿ1=old p.f.angle, Ǿ2=new pf angle

= 504 ( 0.75 - 0.14) [ here, KW=504 because, 630 X 0.8 = 504]
= 307.44 KVAR
say, 300 KVAR bank is required at load end for compansation

Is This Answer Correct ?    15 Yes 4 No

How much KVAr bank reqired for 630 KVA transformer on full load for maintain power factor upto.99..

Answer / engr junaid afrid

Simply says 630/2=315 kvar for your system.

Is This Answer Correct ?    4 Yes 1 No

How much KVAr bank reqired for 630 KVA transformer on full load for maintain power factor upto.99..

Answer / mahendra singh

KVAR = KVA * sin@
KVAR = KVA * sqrt (1-cos@*cos@)
KVAR = 630* sqrt(1-.99*.99)
KVAR = 88.87

Is This Answer Correct ?    1 Yes 3 No

How much KVAr bank reqired for 630 KVA transformer on full load for maintain power factor upto.99..

Answer / sanjay

generally kvar depends upon 33% of full load. please suggest if i m wrong.

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

Why transformer rating in KVA? and Generator also?

6 Answers   Bhel, IEEE, Toyo Denki, Toyo Engineering,


formula for calculation of switchgears(i.e. contactor, fuse, cb, relay etc.), if load current is given?

0 Answers  


describe the Operation of induction generators from bus bars

0 Answers   AMIE,


what is the function of open delta System?

1 Answers  


what is non uniform load

1 Answers  






HAI,I HAVE 6,60KW MOTOR FEEDERS IN MY MCC PANEL.HOW CAN I DO MY SETTINGS FOR OVERLOAD,SHORTCIRCUIT,GROUNGFAULT,INSTANTANEOUS TRIP FUNCTION IN MY 4000A CIRCUIT BREAKER?

1 Answers  


Why NGR is required for 11Kv geneartor in power plant

2 Answers   AB Inc, ABB,


How to size fuse? How to size MCB?

0 Answers  


current transformer balance the power level on both sides. e.g in case of step up, at secondary side voltage rise but current decrease and vice versa in case of step down transformer. but how this power level remains same in case of current transformer and voltage transformer

0 Answers  


What is the classification of hydro projects based on installed capacity?

0 Answers  


WHY HUMMING SOUND OCCURED IN HT TRANSMMISSION LINES ?

26 Answers   GE,


what is the principal of star delta starter?

9 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)