Why short circuit calculation is not required in LT cable
sizing and requiredin HT cable sizing only
Answers were Sorted based on User's Feedback
Answer / sudhanva madhukar mahamuni
Generally LT Cable size are not calculated based on Fault current basis, Due to High Fault current on LT System. For e.g. consider that 2500 kVA Transformer, %Z = 6.25%, 415 Volts at Secondary. Fault Current at Secondary system will be 55.64 kA. Now if we would have to select the Cable size based on Fault current then it would be ---
If √t
A = ----------------- Sq.mm --- For XLPE Cable Aluminum Conductor
0.094
585 sqmm, nearest standard rating of cable is 630 sqmm. Hence Commercially as well as laying point of view the same is not recommended nor as per good engineering practice.
HT Cable Sizing :
Cable sizing based on Fault current is possible In HT System, based practically and commercially point of view. Consider that 11kV system is feeding the power supply. As per IS 2026, 11kV Power system will have max 500MVA Fault Level. It means it will have 26 kA. 300sqmm cable will be sufficient to withstand 26 kA for 1 Sec.
Summary : System Design shall not be strictly as norms, it should be design considering Laying / installation, Practically and Commercially viable.
Regards
Sudhanva Madhukar Mahamuni
electricmahamuni@gmail.com
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / xyz
Short Circuit withstand capacity is to be checked for HT
cables. For LT breaker controlled motor feeders, the cable
impedance reduces short circuit current considerable, hence,
short circuit withstand capacity is not required to be
checked for the rated fault level of the LT motors.
| Is This Answer Correct ? | 3 Yes | 5 No |
How is the Depth of Stator Slot being calculated for Synchronous Generator?
In Single Phase AC Supply,If Voltage between Phase and Neutral is 230V means what will be the Voltage between Phase and Earth?
To check the earth condition (In plug points); the voltage between earth and Neutral is in below 5 volts. Is it correct
Why transformer neutral is earthed
What is the d/f b/w MCCB & MCB
How to work to the x'mer as a induction motor?
From stability point of view,What(higher/lower) should be the value of inertia constant of rotating machines?
What are the different protection systems used to protect the transformer internally and externally?
what is rotatng magnetic field in case of three or multiple phase alternating current machines???
what is cascade speed control device?and how this device control the speed of motors?
I have recently seen a transformer which had two primary terminals and was connected between two lines,i would like to know what kind of transformer is it?short discription about it,any advantages,purpose of usage of the same.............
how to calculate full load current of transformer & induction moter ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)