Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


If a motor of 8.5 KW with same load and using in both Star
& Delta one by one,then which will take more current in
star connected or in delta connected

Answers were Sorted based on User's Feedback



If a motor of 8.5 KW with same load and using in both Star & Delta one by one,then which will ..

Answer / subash nishad

take line voltage is VL and Zs is the impedence of
each phase,
then in case of delta connection ,VP=VL

phase current I(delta)= VL/Zs

we know that in delta connection ,
Line current IL= root 3 times phase
current
so line current I(delta)=root3*VL/Zs
in case of star connection,Vp= VL/root3
phase current I(star)= VL/root3*Zs
weknow that in star connection,
phase current=line current
IL(star)=VL/root3*Zs

so, IL(delta)/IL(star)= root3*VL VL
---------- / ----------
Zs root3*Zs


= root3 *VL root3*Zs
--------- * ----------
Zs VL

= 3

IL(delta) =3*IL(star)

hence, delta connection will take 3 times more current
than star connection..

Is This Answer Correct ?    9 Yes 0 No

If a motor of 8.5 KW with same load and using in both Star & Delta one by one,then which will ..

Answer / virendra

IF motor is started using a delta starter then VP=VL (
Phase voltage is equall to line voltage & Load current Isc
is become root3.Isc.

Now if this motor is connected in star then then VP=VL/root3
& IP= isc /roor3

It clearly shoow that in star connection motor take 1/3
times less current then starting in Delta.

Is This Answer Correct ?    5 Yes 2 No

If a motor of 8.5 KW with same load and using in both Star & Delta one by one,then which will ..

Answer / pillay

What is important is, the motor is designed to operate at
what connection and what voltage.IF it is designed for the
other connection and you powewr it the other way you will
destroy the motor winding or you wont get the intended
power out put.
power is always line voltage X LINE CURRENT x PF x root 3
for 3 phase motor, and you cannot change it.

Is This Answer Correct ?    0 Yes 2 No

If a motor of 8.5 KW with same load and using in both Star & Delta one by one,then which will ..

Answer / benchalli.nagaraj

in STAR the current is more,
Because of

In star: line current = Phase current
In delta: line current =/root 3 phase current

Is This Answer Correct ?    1 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

Compare salient pole and Hndrical rotor machines.

1 Answers  


what is the minimum recommended leakage current of an earthed cable connected to the body or skid of an alternator

0 Answers  


Please explain how to do 'tan-delta test' on AC generator? and where i get clear and brief detail, give any web page address.

1 Answers  


In oil transformer which oil is used & what should be the insulation resistance & heating capacity.

2 Answers  


Dear All, In a 400V power system, ratio of three current transformers installed incoming switchgear is 4000/1. Maximum three phases short circuit current of this system is 48kA. One CT is installed on neutral of upstream transformer (6/0.42kV, solidly earthed) for 51G protection. Would you please inform me about the correct CT ratio of this current transformer (on neutral)?? Thanks a million

2 Answers  


how to calculate the starting current of a motor? gopal

3 Answers   JIPT,


What will happen if the field of synchronous generator is removed when it is in operation with no load?

3 Answers   HJ, UPPCL,


what is the UPS

4 Answers  


What is nichols chart?

0 Answers  


If a Power Transformer Fails and the transformer manufacturer suggest that "Do all electrical test on the transformer?". What are the test to be conducted in this condition?

5 Answers  


Does Rheostat can use for power factor correction?

1 Answers   GOMS,


what happen if turbine trip ,g.c.b not open and excitation on condition?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)