in power station power measuring unit is KW but in
transformer is KVA why?
Answers were Sorted based on User's Feedback
Answer / dipak patil
the tf cu losses are proportion to current and irone or no-
load losses are propotional to voltage rating of
transformer. Since losses once available it is essy to
calculate transformer efficiency. Hence tf rating is given
in KVA insted of KW
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / engr. sumair mir
p.f=kw/kva .... T/f rating is in kva bcoz ,
1- Power factor of the load is not known.....
2- T/F losses depends upon cu- losses(due to current) and
core losses(due to voltage).
due to these resons t/f ratings are in kva.
while for motors and other machines the rating will be in kw
becoz their p.f is known(ranging from .2 to .8 during light
load and peak load period)...
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / srikanta
generally ratings of electrical machines are depends open losses and power factor.
in case of transformer copper loss depend on current and iron loss on voltage but independent of load power factor,hence it's rating is KVA rather than KW.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / mahmood al-ali
1- Any transformer includes core losses and copper losses
2- Core losses are based on input voltage
3- Copper losses are based on current flowing through winding
4- Therefor, total losses are based on voltage in addition to current but not power factor.
Thus, the rating of transformer is done in KVA not in KW
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the minimum voltage require to injure our body?
I have 2 transformers in two different plants, both are without OLTC but i am facing problem of voltage fluctuation at LV side from only one transformer. i have to change its taps manually twice in a day. Another transformer delivering voltage is ok. Please guide me about the problem
how can the active power and reactive power of an alternator be controlled?
what reactive how to maintain
how to calculate IR value of 33KV cable ??
What do you mean by the zone of protection?
why in India it is maintained for exactly 50HZ frequency, why it is not that 49Hz,why it is so?
we can conformed the vector group of the transformer. How?
in dc shunt motor if field winding is shorted then
What Should be the value of Vector Surge angle at Tripping and how to calculate it?
what is the term of desruptive voltage
5 Answers Bhel, Energy Infratech,
what is the difference between transformer and amplifier ??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)