Answer / dipak patil
the tf cu losses are proportion to current and irone or no-
load losses are propotional to voltage rating of
transformer. Since losses once available it is essy to
calculate transformer efficiency. Hence tf rating is given
in KVA insted of KW
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / engr. sumair mir
p.f=kw/kva .... T/f rating is in kva bcoz ,
1- Power factor of the load is not known.....
2- T/F losses depends upon cu- losses(due to current) and
core losses(due to voltage).
due to these resons t/f ratings are in kva.
while for motors and other machines the rating will be in kw
becoz their p.f is known(ranging from .2 to .8 during light
load and peak load period)...
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / srikanta
generally ratings of electrical machines are depends open losses and power factor.
in case of transformer copper loss depend on current and iron loss on voltage but independent of load power factor,hence it's rating is KVA rather than KW.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / mahmood al-ali
1- Any transformer includes core losses and copper losses
2- Core losses are based on input voltage
3- Copper losses are based on current flowing through winding
4- Therefor, total losses are based on voltage in addition to current but not power factor.
Thus, the rating of transformer is done in KVA not in KW
| Is This Answer Correct ? | 1 Yes | 0 No |
What is nichols chart?
why the transformer connected like STAR- STAR, DELTA- DELTA, STAR- DELTA, DELTA-STAR ...? why these connections ,,, explain the advantages these connections?
Why one side of secondary of transformer is earthed, to supply single conductor of electric traction system?
what is work of choke in tube light?
What is the difference between alternator and generator?
Explain the working principle of Synchronous Generator and Assynchronous generator?
What is power factor? How to improve Power factor? draw a circuit diagram showing the connection of power factor improvement equipment to the electrical instillation.
I need to calculate the Battery bank back up for below configuration:- UPS - 120 KVA Battery Bank - 200Ah Volt of each cell - 12 V Total No of cell - 34 No's Can you please help me to get the battery back up time for above configuration...? along with formula
Why design 150Hz in Exciter
how i calculate the size in mm of the LT 4 core cable for 100 HP inductive motor pump
Why the cores of large transformers build up of circular cross section?
whatis mean by voltage?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)