Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Should transformer earthing pit, to be connect to earthing
mat in Substation

Answers were Sorted based on User's Feedback



Should transformer earthing pit, to be connect to earthing mat in Substation..

Answer / niranjan

ยท The system earthing and safety earthing are interconnected and therefore fault current flowing through system ground raises the potential of the safety ground and also causes steep potential gradient in and around the Substation. But separating the two earthing systems have disadvantages like higher short circuit current, low current flows through relays and long distance to be covered to separate the two earths. After weighing the merits and demerits in each case, the common practice of common and solid (direct) grounding system designed for effective earthing and safe potential gradients is being adopted.

Is This Answer Correct ?    3 Yes 0 No

Should transformer earthing pit, to be connect to earthing mat in Substation..

Answer / siva kumar

during fault conditions the fault current fed from transformer neutral.So the earth pit which is connected to neutral has to supply fault current.
supplying of quantity of fault current by earth pit has limitations such as soil type.CIPipe lengh etc.
if you connect neutral earth pit to substation mat, the mat will supply the fault current.

it is just like earth as big water reservoir and water as current. If more and more parlel pipe lines are laid more quantity of water can be dischrged quickly.

Is This Answer Correct ?    1 Yes 0 No

Should transformer earthing pit, to be connect to earthing mat in Substation..

Answer / pankaj agarwal

as the short circuit fault devlops in the system the fault
current flows from fault point into the neutral. in the
absense of interconnection, all the fault current has to
travel through ground which have high resistivity so the EF
current flowing in the system may not be sufficient to
operate the EF trip relay. in the interconnected system EF
current have alternate and less resistive path so fault
gets cleared fast.

Is This Answer Correct ?    1 Yes 0 No

Should transformer earthing pit, to be connect to earthing mat in Substation..

Answer / nipesh

but we do metal glanding in secondary side cable termination in both side, transformer and PCC panel (LT Panel), in this case transformer body earthing and substation earthing both are joint through metal gland, is this safe for transformer and other equipment?

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

how do i work out the Amps of a incommer if i am running 1 37 KW motor and a 0,75 KW motor and some solinoids

0 Answers  


what is the formula for transformer oil?

1 Answers  


What is difference between insulating medium and fault current interruption medium in a switching device.

0 Answers  


How can we define 'Phase'

4 Answers  


what is the reqirred voltage in HT motor to get full RPM on no load test?

0 Answers  


HOW WE CHOOSE EARTH'S POTENTIAL AS ZERO V?

0 Answers  


how copper and aluminium wires or cables are choose for current rating? please provide copper and aluminium wire selection chart for different current rating ?

0 Answers  


what is the difference between LATCH and FLIP FLOP

4 Answers   Wipro,


need to make a report. Need to choose a 3phase induction motor. Load conditions motor will operate in : Maximum Load: 30 Kw Speed: 2950 rpm Ambient temp: 20 cent Supply voltage: 440V Frequency: 50Hz need to look for the safety factor when choosing the motor, went through catalouge found a few, but dont know how to choose the safety factor allowing an extra load something above 30 KW to avoid any harm.

0 Answers  


if z transform lies in ROC then. a)system is stable b)inverse of system is stable c)both system and its inverse are stable.

1 Answers   CCP,


Why a single-phase induction motor not an inherently self-starting machine?

11 Answers   ETC, Hindustan Shipyard,


Explain the laying procedure and laying depth of submarine/subsea power cable for 220/400KV system? Also available cable diameter?

0 Answers   ABB,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)