Answer / niranjan
ยท The system earthing and safety earthing are interconnected and therefore fault current flowing through system ground raises the potential of the safety ground and also causes steep potential gradient in and around the Substation. But separating the two earthing systems have disadvantages like higher short circuit current, low current flows through relays and long distance to be covered to separate the two earths. After weighing the merits and demerits in each case, the common practice of common and solid (direct) grounding system designed for effective earthing and safe potential gradients is being adopted.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / siva kumar
during fault conditions the fault current fed from transformer neutral.So the earth pit which is connected to neutral has to supply fault current.
supplying of quantity of fault current by earth pit has limitations such as soil type.CIPipe lengh etc.
if you connect neutral earth pit to substation mat, the mat will supply the fault current.
it is just like earth as big water reservoir and water as current. If more and more parlel pipe lines are laid more quantity of water can be dischrged quickly.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pankaj agarwal
as the short circuit fault devlops in the system the fault
current flows from fault point into the neutral. in the
absense of interconnection, all the fault current has to
travel through ground which have high resistivity so the EF
current flowing in the system may not be sufficient to
operate the EF trip relay. in the interconnected system EF
current have alternate and less resistive path so fault
gets cleared fast.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / nipesh
but we do metal glanding in secondary side cable termination in both side, transformer and PCC panel (LT Panel), in this case transformer body earthing and substation earthing both are joint through metal gland, is this safe for transformer and other equipment?
| Is This Answer Correct ? | 1 Yes | 0 No |
Why only plate(copper) Earth pit given for neutral earthing? why not pipe(G.I) Earth pit?
what does the word synchronous mean in 'synchronous machine'
A 60w bulb & a room heater are connected in series.if 60 w bulb is replaced by 100w then what will be the effect on heater out & why?
IAM GOING TO ERECT THE STREET LIGHT.,, I NEED HOW TO CALCULATE LUX., ILLUMINATION.,AND ALL
PLEASE ANYBODY HAVE ELECTRICAL CIRCUIT DIAGRAM FOR CHMER PULSE CD 60M SPARKING MACHINE.PLEASE MAIL ME SUPRIYAAYYAPPAN@YAHOO.CO.IN.
how a resistor resists to flow the current?how an inductor oppses the sudden change in current?how a capacitor opposes a DC voltage.
0 Answers Hindustan Unilever Limited,
what is the current limit of lighting arrester ?
what is difference between earthingpits,earthing grid & earthing mess?
I am having 120KVA UPS,which is connected to DG & normal power. What is the power drawn by this system when system is running on DG ????
Why need 3phase machine double earthing?
Determine the minimum cable size for a 28A single phase final sub circuit originating from the distribution board supplied by three phase submain. The route length of the final sub circuit is 54 m. Assume 1% voltage drop in the consumer's mains. Submain specification: Cable: 50mm2 4 core V75 copper; Route length 42m; Maximum demand 135A per phase
How to model "IF ELSE" statement in matlab simulink?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)