Should transformer earthing pit, to be connect to earthing
mat in Substation

Answers were Sorted based on User's Feedback



Should transformer earthing pit, to be connect to earthing mat in Substation..

Answer / niranjan

ยท The system earthing and safety earthing are interconnected and therefore fault current flowing through system ground raises the potential of the safety ground and also causes steep potential gradient in and around the Substation. But separating the two earthing systems have disadvantages like higher short circuit current, low current flows through relays and long distance to be covered to separate the two earths. After weighing the merits and demerits in each case, the common practice of common and solid (direct) grounding system designed for effective earthing and safe potential gradients is being adopted.

Is This Answer Correct ?    3 Yes 0 No

Should transformer earthing pit, to be connect to earthing mat in Substation..

Answer / siva kumar

during fault conditions the fault current fed from transformer neutral.So the earth pit which is connected to neutral has to supply fault current.
supplying of quantity of fault current by earth pit has limitations such as soil type.CIPipe lengh etc.
if you connect neutral earth pit to substation mat, the mat will supply the fault current.

it is just like earth as big water reservoir and water as current. If more and more parlel pipe lines are laid more quantity of water can be dischrged quickly.

Is This Answer Correct ?    1 Yes 0 No

Should transformer earthing pit, to be connect to earthing mat in Substation..

Answer / pankaj agarwal

as the short circuit fault devlops in the system the fault
current flows from fault point into the neutral. in the
absense of interconnection, all the fault current has to
travel through ground which have high resistivity so the EF
current flowing in the system may not be sufficient to
operate the EF trip relay. in the interconnected system EF
current have alternate and less resistive path so fault
gets cleared fast.

Is This Answer Correct ?    1 Yes 0 No

Should transformer earthing pit, to be connect to earthing mat in Substation..

Answer / nipesh

but we do metal glanding in secondary side cable termination in both side, transformer and PCC panel (LT Panel), in this case transformer body earthing and substation earthing both are joint through metal gland, is this safe for transformer and other equipment?

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

In AC if the direction of current keeps reversing every half cycle, how does it propogate through the transmission lines?

0 Answers  


i have been tasked with a design of protection, metering and control(PMC) relay panel extension to accommodate all PMC relays.There is an already existing panel where this one will be built.What are the design aspects for this kind of project? thank you.

0 Answers  


What is the difference between EXE and EXD

1 Answers  


what is a vector protection in transformer

0 Answers  


when elecromagnatic waves are propogated in a wave guide?

0 Answers  






how to select the automotive wire size by mathematical calculation. for xenon headlamp with ballast. the ballast given data voltage 10-17v,current permenant 6amp, run up phase is 15amp, peak at swicth on max 400micro sec is 40amp.the sum of cable resistance is 150mohm.please provide referenc document if any for relating the peak at switch on current,time & wire wire size

0 Answers   Tyco,


what is the thumb rule or formula for cable size and current ratings

1 Answers  


how calculate kva in to kw

1 Answers  


if an alternator or turbine using fuel to produce ele energy and we didn't connect load to the ends then where was gone the ele energy

2 Answers  


how motor should be connected i.e star-delta or star-star or delta-delta ?

3 Answers   GSE,


what is the meaning of the HT LT transformer?

10 Answers   Sify,


why ie corona losses in tranmission line

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)