How can we calculate earth mat conductor size ..? & give
the formula to determine earth conductor size?
Answers were Sorted based on User's Feedback
Answer / zan
Several variable factors are involved in the
design of earthing mat conductor.Therefore, earthing mat
for each substation has to designed individually usually.
The earthing mat has to be designed for the site conditions
to have a low overall impedance and a current carrying
capacity consistent with the fault current magnitude. The
parameter listed below influence the design of earthing mat:
• Magnitude of fault current;
• Duration of fault;
• Soil resistivity .
• Resistivity of surface material;
• Shock duration;
• Material of earthing mat conductor and
• Earthing mat geometry.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / parag shukla
It is basically depends on the soil resistivity & system
load. You can calculate the current for this load from that
calculate the conductor size & earth mat calculations
| Is This Answer Correct ? | 3 Yes | 5 No |
We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our electrical load . the issue is though we have Glanded the cable both the end also givan the earthing to the panel both the end we are facing a heavy sparking at the gland side. what could be the reason.
I have a situation to design sub-Distribution board/Panel meant for feeding power sockets. In the incomer CAN i Take TP MCCB with Neutral Link and All the outgoing feeders with to sockets with TP MCCB and Neutral Link? P.S : My System is IT Earthing
what is the impedence
what is ic 01,ic 06 ?is it types of cooling?
what is the advantage of using 3 phase line rather than using 2 phase line?
What is boucholz relay and the significance of it in to the trformer?
Is it acceptable of installing an earth pit in planters area where bare copper cable, earth rod and connection are susceptible to corrosion due to water?
How are load losses and no-load losses measured at site in a DG set?
i have a 1500kVA transformer what is the kWH meter i need to use?
0 Answers HP, L&T, Mohammed Harasani Architects,
if name plate detals of a motor or any other is missing then how to find it
Define peak overshoot.
What is difference is of VSD,VFD,VSDS, are they the same as the direct current to control dc using above mention
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)