How can we calculate earth mat conductor size ..? & give
the formula to determine earth conductor size?
Answers were Sorted based on User's Feedback
Answer / zan
Several variable factors are involved in the
design of earthing mat conductor.Therefore, earthing mat
for each substation has to designed individually usually.
The earthing mat has to be designed for the site conditions
to have a low overall impedance and a current carrying
capacity consistent with the fault current magnitude. The
parameter listed below influence the design of earthing mat:
• Magnitude of fault current;
• Duration of fault;
• Soil resistivity .
• Resistivity of surface material;
• Shock duration;
• Material of earthing mat conductor and
• Earthing mat geometry.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / parag shukla
It is basically depends on the soil resistivity & system
load. You can calculate the current for this load from that
calculate the conductor size & earth mat calculations
| Is This Answer Correct ? | 3 Yes | 5 No |
What are the consequences in using existing step up transformer (primary 6.6kv/175A, secondary 480v/2405A) for step down transformer to have a 6.6kv output?
What is ZCT? it operating principle and how is work with RCCB (residual current circuit breaker)?
what is the value will come when megger the phase to phase ,phase to neutral ,phasae to ground ?
star delta starter single line digram
What is x/r ratio?
Why earthing done?
Which loss in DC machine is maximum?
How to calculate amount of copper used in a motor (AC&DC), generator and transformer? Datasheet provides power rating and mass of the equipment....can we somehow use this available info.
can we use engine degreaser for electrical motors?
For refrigerators the motor current is raised beyond its rating on both conditions when the voltage of the system is more(say 270v) than the rated voltage(220v) as well as when the voltage of system is less(say 160v) than normal voltageof 220v, why explain?
0 Answers Electrical Tech, UPSE,
What is Surge Capacitor? Why it is require in Generator Circuit Breaker,inspite of surge arrester?
In DC while we mention the voltage we are using -48V but in case of AC we mention only 230V not -230V, why we using -48V not 48V
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)