Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

How can we calculate earth mat conductor size ..? & give
the formula to determine earth conductor size?

Answer Posted / zan

Several variable factors are involved in the
design of earthing mat conductor.Therefore, earthing mat
for each substation has to designed individually usually.
The earthing mat has to be designed for the site conditions
to have a low overall impedance and a current carrying
capacity consistent with the fault current magnitude. The
parameter listed below influence the design of earthing mat:
• Magnitude of fault current;
• Duration of fault;
• Soil resistivity .
• Resistivity of surface material;
• Shock duration;
• Material of earthing mat conductor and
• Earthing mat geometry.

Is This Answer Correct ?    7 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is the affect of earth's magnetic field on the frequency used in aircraft???

1998


Briefing the effects of ASR and ACR of a double closed-loop speed regulating system.

2238


what r PID controllers?why they r used?what is there purpose?plz Explain in detail

2068


it is possible to rotate the DG engine dc starter with wrong polarity connections? why?

2250


1.WHAT IS A SMART CAPABLE DB ( DISTRIBUTION BOX) ? 2. HOW TO DECIDE THE TYPE OF DB TO BE USED ( RECESSED/ PLUG TYPE/ SMART ETC ETC? 3. WHAT IS MILLENEUM BUS BAR USED IN DB? 4.DIFFERENTIATE MCCB AND MCB.

1832


Why dry type cast resin transformers tap link blast in HV side while power shut down times on load?

2318


how to measure earth resistance of a substation

3314


How to calculate energy stored in an inductance?

1137


What is relation between transmission lines & Communication lines ?

2189


what is the soft starter principle? how is connection diagram? what is the procedure for checking the connection?

2158


What are the advantages and disadvantages of the dc motors?

1129


i installed 100kva ups. what KVA genset they should provid in input side? plz any update formula or ans with reason.

2330


If an electrical component has a positive temperature coefficient, how come such components have high power losses due to heat if current decreases when resistance increases? assuming power given by I^2*R whereby the Resistance is infinite.

1072


Please clarify, 1. Is it required to lay two runs of GI wire along with Armoured LT cable if it is laid between one big mains (63Amps TPN SDF) to small main (32A TPN SDF) with proper glanding termination? 2. If the armoured cable with proper glanding is laid from DB to CNC machine, is it required to run two runs of body earthing to the Machine from DB? 3.If the armoured cable with proper glanding is laid from Substation to Hangar, distance is approx. 100 mtrs, is it required to do earthing at shop area though the primary termination at substation is earthed through gland.

2024


Why do we apply both Differential and REF (HV and LV) protection schemes on YNyn configuration of a transformer?

2128