Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

How can we calculate earth mat conductor size ..? & give
the formula to determine earth conductor size?

Answer Posted / prasad

for bolted joints cross section Area of the conductr
A=0.0013*I*sqrt(t),
for welded joints cross section Area of the conductr
A=0.011*I*sqrt(t),

I - Fault current (KA) = Fault MVA/ (sqrt3 * system KV)
t - Duration of time

Is This Answer Correct ?    3 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Best way to measure the Soil resistance of rocky soil, three probe method and four probe method

1880


I have a relay contact rated at 220v dc which is supplied with a 24vdc from the panel,for it to trip the dampers(24vdc).What if the application of the relay changes so that it should work at its rated 220vdc then will it work at 24vdc supply given or any other consideration needs to be taken .....

2018


On a 6 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 42 AH). What Shall be the current rating of DC MCB ?

2573


in dc shunt motor if field winding is shorted then

1791


In what condition the HT fuse breakes?

1954


List few applications of d.c series motor?

1090


what is the difference b/w absolute encoder and incremental encoder?

2023


Did RMU have ct and pt ?

1315


What is tan delta & PPM in transformer? and whats its IS value?

2081


can we use engine degreaser for electrical motors?

1709


Why can't we parallel Voltage transformer secondary circuits?

1554


how a flip flop can be used as a latch?

1937


How to calculate or formula to calculate rhe power in 2 phase system ??

1450


hello friend i wish to study a course related to the electrical construction, controlling and monitoring , which course i want to study? pls give me the name of institute?

1745


please send 5yearje solved papers on my email himmatsinghnathawat@gmail.com

1871