How can we calculate earth mat conductor size ..? & give
the formula to determine earth conductor size?
Answer Posted / prasad
for bolted joints cross section Area of the conductr
A=0.0013*I*sqrt(t),
for welded joints cross section Area of the conductr
A=0.011*I*sqrt(t),
I - Fault current (KA) = Fault MVA/ (sqrt3 * system KV)
t - Duration of time
| Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
pls tell me function of closing coil of A.C.B.
any one can explain the stages of a knee point which is taken during ct magnetising curve.
What is the Current equation in series RLC circuits.
what are the reasons of CT circuit faulty in busbar protection scheme?
AL=0B9H,bl=75H, ADD AL,BL AL=____________? CF________? OF___________?
Give details on how you intend to handle a challenging position you are posted to manage unexpectedly as a company staff?
DEFINE BREAKING CAPACITY OF BUSBAR & HOW IT IS CALCULATED?
what is submersible pump?what is different between motor and sub motor?
If 22 KV HT line, Current transformer is 25/5 then how to calculate multiplying factor.
how invertor convert the dc into ac give brif detail
what are factors comes under relay setting (distance relay 7sa52) under OPEN DELTA VTs connection??
When will you multiply and devide with derating factors to the actual value while sizing the cable?
What is the different between conventional MCC and intelligent MCC? Common controller or controller for each bucket
What is the meaning of HT Trivector Meter ?
describe the fully control circuit diagram of ac drives