Answers were Sorted based on User's Feedback
Answer / iamdon
A 50-Hz designed transformer can be used at 60-Hz system
but a 60-Hz designed transformer cannot be utilized at 50-
Hz system.
Because in later case, the transformer windings(primary and
econdary)will draw approximately 20 % greater current than
the rated one.More current flowing will produce more
winding heating loss.The temperature of winding rises
(Beacuse cooling system was designed for rated current
which was lower as compared to present higher value of
current at low frequency operation)and it get burnt.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 8 Yes | 3 No |
For a transformer the voltage is proportional to the product of flux and frequency.
case-I
Voltage = constant
Frequency = increased from 50 to 60Hz i.e. change by 120%
For Transformer:
Voltage = flux * frequency * K; k is a constant
so when frequency increases by 120% flux decreases to 83.3% Now;
Hysteresis loss = flux^2 * frequency^2 * T; T is constant
At 50 Hz
Hy. Loss@50 = flux^2 * Frequency^2 * T
At 60 Hz
Hy. Loss@60 = (.833flux)^2 * (1.2Frequency)^2 * T
On evaluation:
Hysteresis loss@50Hz = Hysteresis loss@50Hz
Eddy Current Loss
Eddy C. L. = flux^1.6 * f * C; C is a constant
Eddy@50 HZ = flux^1.6 * f * C
Eddy@60 Hz = (.833flux)^1.6 * 1.2F * C
On evaluation;
Eddy@60Hz = 0.895 * Eddy@50HZ
So it is seen that a 50HZ transformer when operated at at 60Hz has same hysteresis loss eddy current decreases. As the core loss decreases the transformer can be safely operated.
But if a 60Hz transformer is operated at 50Hz, then just the reverse of above the core loss i.e. eddy current loss will increase and hence the core loss will go high; hence not advisable to operate.
| Is This Answer Correct ? | 0 Yes | 0 No |
How many current ratings of MCB's are in the market? e.g: 1A, 2A, .......upto.
what is difference between low voltage and high voltage
How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side
what happen if power factor goss to above unity (one) ? of any electrical system or motor.
sir, in a industry present pf is 0.54 pf 25hp power is there its want improve 0.9 pf. which suitable capacity capacitor is suitable please inform me.
if we supply DC power to AC transformer then what its result?
What is the function of the generator exciter?
through which medium return supply given to alternator please answer in details
why the voltage level is changed when the unearth cable is earth
why HV test for cables?.why 0.7times?
1 Answers Bosch, Prince Food Products,
why fuse is not applicable for nutral and what will happen when it applied.
how we protect the motor & what are the components required for that ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)