Can a 50-Hz designed transformer be used at 60-Hz system?
Is the same remains true, when a 60-Hz designed transformer
be used at 50-Hz system? Consider only frequency variation.
The voltage remains as rated value in all cases.
Justify the answer.
Answers were Sorted based on User's Feedback
Answer / iamdon
A 50-Hz designed transformer can be used at 60-Hz system
but a 60-Hz designed transformer cannot be utilized at 50-
Hz system.
Because in later case, the transformer windings(primary and
econdary)will draw approximately 20 % greater current than
the rated one.More current flowing will produce more
winding heating loss.The temperature of winding rises
(Beacuse cooling system was designed for rated current
which was lower as compared to present higher value of
current at low frequency operation)and it get burnt.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 8 Yes | 3 No |
For a transformer the voltage is proportional to the product of flux and frequency.
case-I
Voltage = constant
Frequency = increased from 50 to 60Hz i.e. change by 120%
For Transformer:
Voltage = flux * frequency * K; k is a constant
so when frequency increases by 120% flux decreases to 83.3% Now;
Hysteresis loss = flux^2 * frequency^2 * T; T is constant
At 50 Hz
Hy. Loss@50 = flux^2 * Frequency^2 * T
At 60 Hz
Hy. Loss@60 = (.833flux)^2 * (1.2Frequency)^2 * T
On evaluation:
Hysteresis loss@50Hz = Hysteresis loss@50Hz
Eddy Current Loss
Eddy C. L. = flux^1.6 * f * C; C is a constant
Eddy@50 HZ = flux^1.6 * f * C
Eddy@60 Hz = (.833flux)^1.6 * 1.2F * C
On evaluation;
Eddy@60Hz = 0.895 * Eddy@50HZ
So it is seen that a 50HZ transformer when operated at at 60Hz has same hysteresis loss eddy current decreases. As the core loss decreases the transformer can be safely operated.
But if a 60Hz transformer is operated at 50Hz, then just the reverse of above the core loss i.e. eddy current loss will increase and hence the core loss will go high; hence not advisable to operate.
| Is This Answer Correct ? | 0 Yes | 0 No |
Is an SCR semi controlled device?
HOW TO CALCULATE EARTHING SIZING?
what is anti-pumping relay and the significance of it in a switcgear cb control system?
what are the deffects for failure of PLC?
what is dedicated earthing
2 Answers Apollo Power, Student,
Y phase plates are used in transmission line??? what is there need???
What do you mean by passive circuit elements and why these are called passive?
Is it any dc fuses availbale in market? can we use one fuse for both AC & DC ?
For an induction motor wat is the loading/unloading cycle duration or interms of L/UL ratio/ percentage?
why ahould you show client/engineer activities clearly on the project plan
At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC 54A as per the nameplate. At the time of starting it draws 840A instead of 390A (7.2%). As per the data sheet also its 390A starting current. it thru a dol starter from the MCC. can anyone tell what is the problem in the motor
if the voltage across the lamp drops by 1%, the power drawn will be reduced by how many %?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)