At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC
54A as per the nameplate. At the time of starting it draws
840A instead of 390A (7.2%). As per the data sheet also its
390A starting current. it thru a dol starter from the MCC.
can anyone tell what is the problem in the motor
Answers were Sorted based on User's Feedback
Answer / ranjan prasad
From the question motor terminal connection is not known.
However this problem may arise if you will connect the
motor in delta instead of star. First check the terminal
connection of motor, if it is in star, connect in the same
manner.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / kannapa
do not use dol starer above 2.2kw rated motors
use star to delta starter it can withstand.
check also connections.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / r.v.giribabu
First Check the healthyness of the motor.
1. Check the winding resistence
2. Check insulation resistance using megger.
3. Check the bearing and apply the lubricant as applicable.
4. Check the healthyness of connected load.
Follow above steps adn yoiu will identify the problem.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / wani y.s.
First Check the healthyness of the motor -
1. Check the winding resistence
2. Check insulation resistance using megger.
3. Check the bearing and apply the lubricant as applicable.
4. Check the healthyness of connected load.( It should not
locked etc.)
5. If all above is OK. Then remove the motor from load &
ensure it is starting in ideal condition.( Hope connections
you are following up as given on the nameplate)
If it is starting in no load that means load GD squre is
high. Motor is taking longer time to start.You have to
select proper heavy duty DOL starter to withstand the
longer starting time. But ensure that motor is having
thermal time capacity to withstand this time.
7. You can also go for VFD as a starter this will definetly
will solve your problem no need to take care of thermal
time of the motor. Only select proper VFD to suit starting
torque of your application.
| Is This Answer Correct ? | 0 Yes | 1 No |
pl. check motors connection in terminal box if it is
connected in star then current may increased.
| Is This Answer Correct ? | 5 Yes | 13 No |
Generation of voltage for each phase are same of a turbogenerator.Although the short circuit current flow when two phase of turbogenerator are shorted(where current can't flow without potential difference),why?
what is the basis for selection of Protection CT class ? How anyone can decide whether to go for 5P10 or 5P20 ?
Hi to all... I Want Weight Details of the alternator for making free power energy.
what is the difference between current rating and breaking current of an MCCB? and for a known load how to calculate the current rating of a MCCB?
How to measure the capacity/rating of a distribution transformer in KVA?
What are the various types of BUSBAR Schemes? explain each
what is active network?
what are the applications of transistors with low dc gain, high dc gain and medium dc gain( beta)?
Why do we use 36KV LAS for 33kv line and 9KV LAS for 11KV line?
how much current (in MW)can be carried max. through S/C dog & Panther Conductor ?
What is the fundamental cause of transients in power system?
Why Closing coli supervision is not required for Circuit breaker.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)