Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC
54A as per the nameplate. At the time of starting it draws
840A instead of 390A (7.2%). As per the data sheet also its
390A starting current. it thru a dol starter from the MCC.
can anyone tell what is the problem in the motor

Answers were Sorted based on User's Feedback



At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC 54A as per the nameplate. At the time of ..

Answer / ranjan prasad

From the question motor terminal connection is not known.
However this problem may arise if you will connect the
motor in delta instead of star. First check the terminal
connection of motor, if it is in star, connect in the same
manner.

Is This Answer Correct ?    7 Yes 3 No

At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC 54A as per the nameplate. At the time of ..

Answer / kannapa

do not use dol starer above 2.2kw rated motors

use star to delta starter it can withstand.

check also connections.

Is This Answer Correct ?    1 Yes 0 No

At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC 54A as per the nameplate. At the time of ..

Answer / r.v.giribabu

First Check the healthyness of the motor.

1. Check the winding resistence
2. Check insulation resistance using megger.
3. Check the bearing and apply the lubricant as applicable.
4. Check the healthyness of connected load.
Follow above steps adn yoiu will identify the problem.

Is This Answer Correct ?    0 Yes 0 No

At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC 54A as per the nameplate. At the time of ..

Answer / wani y.s.

First Check the healthyness of the motor -

1. Check the winding resistence
2. Check insulation resistance using megger.
3. Check the bearing and apply the lubricant as applicable.
4. Check the healthyness of connected load.( It should not
locked etc.)
5. If all above is OK. Then remove the motor from load &
ensure it is starting in ideal condition.( Hope connections
you are following up as given on the nameplate)
If it is starting in no load that means load GD squre is
high. Motor is taking longer time to start.You have to
select proper heavy duty DOL starter to withstand the
longer starting time. But ensure that motor is having
thermal time capacity to withstand this time.
7. You can also go for VFD as a starter this will definetly
will solve your problem no need to take care of thermal
time of the motor. Only select proper VFD to suit starting
torque of your application.

Is This Answer Correct ?    0 Yes 1 No

At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC 54A as per the nameplate. At the time of ..

Answer / atul pradhan

pl. check motors connection in terminal box if it is
connected in star then current may increased.

Is This Answer Correct ?    5 Yes 13 No

Post New Answer

More Electrical Engineering Interview Questions

What is Phase margin?

0 Answers  


What is thyristor?

13 Answers  


what is formula to cal cute earth pit numbers and size of earth strip used in earthing?

0 Answers  


Wy transformer ratings are in multiple of 11 always?

2 Answers  


Is it recommended to apply H.pot test for new cables segments after terminations or joints, however, this cable has been tested before at the manufactor by the vendor ? or only we can apply megger tests ?

1 Answers   Centroid,


What is transmittance?

0 Answers  


lightning arrester rating selection procedure: (line to line voltage(kV)/(squ.root of 3))*squ.root of 2. now the question is, IS this above formula correct for both STAR and DELTA connected system???

1 Answers  


what is the maximum rating(KVA) of transformer can be used in distribution side..(11KV/440v) and why??

1 Answers   Jindal,


Differences between 415v ac and 440v ac

3 Answers  


what are the major difference between 3phase 3wire and 3phase 4wire trivector meter?

2 Answers   L&T, NTPC,


for 8 mva 33/11 kv transformer what will be the setting of differential relay on which it trip & what is the HF setting in this relay

2 Answers  


What is the difference between Analogue Addressable Systems and intelligent Addressable Systems

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)