At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC
54A as per the nameplate. At the time of starting it draws
840A instead of 390A (7.2%). As per the data sheet also its
390A starting current. it thru a dol starter from the MCC.
can anyone tell what is the problem in the motor
Answers were Sorted based on User's Feedback
Answer / ranjan prasad
From the question motor terminal connection is not known.
However this problem may arise if you will connect the
motor in delta instead of star. First check the terminal
connection of motor, if it is in star, connect in the same
manner.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / kannapa
do not use dol starer above 2.2kw rated motors
use star to delta starter it can withstand.
check also connections.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / r.v.giribabu
First Check the healthyness of the motor.
1. Check the winding resistence
2. Check insulation resistance using megger.
3. Check the bearing and apply the lubricant as applicable.
4. Check the healthyness of connected load.
Follow above steps adn yoiu will identify the problem.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / wani y.s.
First Check the healthyness of the motor -
1. Check the winding resistence
2. Check insulation resistance using megger.
3. Check the bearing and apply the lubricant as applicable.
4. Check the healthyness of connected load.( It should not
locked etc.)
5. If all above is OK. Then remove the motor from load &
ensure it is starting in ideal condition.( Hope connections
you are following up as given on the nameplate)
If it is starting in no load that means load GD squre is
high. Motor is taking longer time to start.You have to
select proper heavy duty DOL starter to withstand the
longer starting time. But ensure that motor is having
thermal time capacity to withstand this time.
7. You can also go for VFD as a starter this will definetly
will solve your problem no need to take care of thermal
time of the motor. Only select proper VFD to suit starting
torque of your application.
Is This Answer Correct ? | 0 Yes | 1 No |
pl. check motors connection in terminal box if it is
connected in star then current may increased.
Is This Answer Correct ? | 5 Yes | 13 No |
what is high - pot test. what's its use?????
how to i get B licence,i am completed BE electircal and electronics engineering.i want to konw the proceduure to get b licence
Both generator parallel condition shared load equally but one genrator taking ampere more than the other what are all the causes to make like this
What is load shedding?
what happens if commutator is removed in an dc machine?
From past few months I am getting lagging pf even though sufficient capacitors used in circuit. Where is the problem pls answer
What is VCB? where it is installed at SP. What is SP?
What is icu and ics in Acb and how many time icu or ics passes from breaker?
When a 25kV line touches the train, will passenger get shock?
if 40 watt bulb has higher resistance then a 100watt bulb then according to joul farmula p=I^2R the 40 watt bulb more power consume then 100 watt bulb.
Merits & Demarits of Oil circuit & Air circuit breakers ?
I want to do a mini project. Now I'm studying in 6th semis tor EEE Engineering.