At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC
54A as per the nameplate. At the time of starting it draws
840A instead of 390A (7.2%). As per the data sheet also its
390A starting current. it thru a dol starter from the MCC.
can anyone tell what is the problem in the motor
Answers were Sorted based on User's Feedback
Answer / ranjan prasad
From the question motor terminal connection is not known.
However this problem may arise if you will connect the
motor in delta instead of star. First check the terminal
connection of motor, if it is in star, connect in the same
manner.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / kannapa
do not use dol starer above 2.2kw rated motors
use star to delta starter it can withstand.
check also connections.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / r.v.giribabu
First Check the healthyness of the motor.
1. Check the winding resistence
2. Check insulation resistance using megger.
3. Check the bearing and apply the lubricant as applicable.
4. Check the healthyness of connected load.
Follow above steps adn yoiu will identify the problem.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / wani y.s.
First Check the healthyness of the motor -
1. Check the winding resistence
2. Check insulation resistance using megger.
3. Check the bearing and apply the lubricant as applicable.
4. Check the healthyness of connected load.( It should not
locked etc.)
5. If all above is OK. Then remove the motor from load &
ensure it is starting in ideal condition.( Hope connections
you are following up as given on the nameplate)
If it is starting in no load that means load GD squre is
high. Motor is taking longer time to start.You have to
select proper heavy duty DOL starter to withstand the
longer starting time. But ensure that motor is having
thermal time capacity to withstand this time.
7. You can also go for VFD as a starter this will definetly
will solve your problem no need to take care of thermal
time of the motor. Only select proper VFD to suit starting
torque of your application.
| Is This Answer Correct ? | 0 Yes | 1 No |
pl. check motors connection in terminal box if it is
connected in star then current may increased.
| Is This Answer Correct ? | 5 Yes | 13 No |
What do you mean by dependent and independent voltage sources?
how do u get less voltage in star connection
what maximum load will take a aluminum cable of 50mm 4 core.
l&t switch FN 63 handle position can we change
what is the meaning of electrical maintenance?
3 Answers GE Healthcare, MAHINDRA,
What is difference between ON delay and OFF Delay Timer?
What are types of central ac plants?
Fot testing new star-delta 132 kw motor in electrical worshop.we should check in star or delta connection as we do not have higher capacity cable in worshop?
we r having 3 core 3 1/2, 4 core cables how we can know this cable has to be used for this purpose?
can we use inductor in case of d.c.,if yes then what will happen in circuit
which connection is there in a rotor of the motor
2 Answers All Trades Electrical, HAL,
Why we are using only Dyn11 tranformer in distribution system but not using a Dyn1 in distributing system?why not and advantage and disadvantage in both
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)