Classical power system stability was mainly focussed on
rotor angle stability but modern power system stability has
more focus on voltage stability.Why?
Answers were Sorted based on User's Feedback
Answer / iamdon
Majority of blackout/grid failure now a days is due to
voltage instability phenomenon.
This is because Modern power system is very vast and
interconnected to form a grid network.Also generation is
not sufficient to meet the load demand which is incresing
rapidly, due to which load end voltage drops.To maintain
load end voltage and power factor within permissible limits
shunt capacitors are used extesively at almost all load bus
bars(Over compensation),which has detrimental effect on
voltage stability.
At the time of peak load(load increase),the voltage at the
load end decreased so reactive power supplied by shunt
capacitors also reduced.So when we have most need of
reactive power supply,the shunt capacitor prove less
capable.
That's why modern power system satbility problem shifts
towards voltage stability.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / arvind
in todays time also rotor angle as well as voltage
stability anlaysis are been in focused, if rotor angle is
not into consideration then why so much transient analysis
is into picture.
| Is This Answer Correct ? | 1 Yes | 0 No |
Yes...Arvind.
Your proposition is right.
I had just made a relative analysis with two stabilities
involved.It does not means that the rotor angle is of no
importance today.It just establish the fact that now we
MORE FOCUSSED towards volyage stability.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dharmesh
actualy both are cosider in today's power system the difference is rotor angle is for protection of generator and voltage regulation is for load regulation.
| Is This Answer Correct ? | 1 Yes | 0 No |
Describe kW and kva and difference between
what is the advantage of pwm pulse compare to squarewave pulse.
how we can calculate power factor without knowing current in 230v 100w load ?
whether Transformer is singly excited or doubly excited machine?
How will calculate losses in an multi core Aluminium LT cable of different sizes & upto what length we can use a LT Cable ?
1.Why we use choke?If we use for high starting voltage then different type choke gives different voltage. Is it correct?
What will happen if we do not provide earthing to the newtral of a power system ?
what is the difference between power and distribution transformer?
32 Answers L&T, VJTI, Wenke Electricals,
Classify drilling machines.
why the altrnator(AVR) not showing the any voltage after making the new winding and insulation?
Dear sir, In our plant have Station Transformer having capacity,i want to know, why LV side 40 - 40MVA is given? & how we can get 6.3 KV supply from tertiary(i.e. Open delta connection), Vector Group YNyn0 - yn0 +d MVA Rating 80MVA / 40 - 40MVA + 26.7MVA Voltage rating 420 (Tap range +6,to -10)81.25% /11.5KV - 11.5KV +6.3KV
What happened if C.T mount at any cable or Bus bar in wrong direction . C.T going on proper work or not . C,T direction is essential thing to properly work.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)