HOW DO I CALCULATE OVER LOAD RELAY & CONTACTOR IN DOL
STARTER?
& in dol why it is require circuit breaker?
Answers were Sorted based on User's Feedback
Answer / x man
for OLR---It has to be Motor full oad current
for Contactor--it has to be 1.5 timmes the motor rated
current.
Circui breaker is used to protect the circuit.
for A tYPR 2 cordination these three componenrs are needed
in the circuits
| Is This Answer Correct ? | 13 Yes | 6 No |
Answer / ermias solomon
in OLrelay 115%*motor name plate current
for contactor use
NEMA table by ermias solomon
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / christopher pino
Refer to NFPA 70 - NEC 2005 (Article: Motor Protection) for
sizing and other consideration.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / barkha
In case of DOL Starter overload relay range depend on full
load current(flc) of the motor it is 2-3 times of flc &
also keep in mind the fuse rating of the motor
| Is This Answer Correct ? | 11 Yes | 15 No |
Answer / nikhil chugh
THE CONTACTOR RATING SHOULD BE 3.5 TIMES GREATER THEN THE
MOTOR CURRENT RATING FOR SMOOTH RUNNING OF THE MOTOR WITH
PANEL
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / k.suresh
motor full load ampes & 6 time higher select OLR AND
Contactor.
| Is This Answer Correct ? | 11 Yes | 27 No |
how can i improve the power factor in domestic (230v)
do we people experience any shock if we catch any one of the three phases (R Y B)in air with out touching ground.
What is the Diff. btw Manule Pull Station & Manule Abort Station Switches used in FM200 System??
What is relation bet kvar & microfarad
Why does the power consumed is always constant even if a fan speed is altered?
power is the product of voltage and current.so we can measure the value of power just by using ammeter and voltmeter.......then why do we use a wattmeter?
we often use the word HT (high tension) line.or we say HT switch gear, whats does HT basically mean. is it different from high voltage.
What are series and parallel isolators?
If the secondary winding will be open in current transformer, how to damage the insulators
Whats the minimum value for I.R. that can be allowed for HT & LT alternators for operation?
Can the efficiency of transformer be measured with the help of wattmeter readings taken at primary and secondary side? Support the answer.
What are the advantages of a three-phase system over a single-phase system?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)