Can the efficiency of transformer be measured with the help
of wattmeter readings taken at primary and secondary side?
Support the answer.
Answers were Sorted based on User's Feedback
Answer / iamdon
No,Transformer efficiency measured with the help of
wattmeter can't be reliable.
The reason is
The efiiciency of transformer is very high (order of 98.5-
99+)% due to static nature of it.The error associated with
ordinary wattmeter is in the range of 1-2 % .Under this
condition the readings taken cann't be reliable.
The efiiciency is measured with the help of data taken from
two tests namely
Open circuit test--indiaction of core loss
Short circuit test--indication of copper loss.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / dabangg
NO . TRANSFORMER READING IS IN KVA SO WEW CANT TAKE A
READING IN WATTMETER
| Is This Answer Correct ? | 0 Yes | 3 No |
This is about the recent problem that we have faced in our project site. We have 6/7.5 MVA. 66/11kV three phase star - star power transformer. The neutral was solidly connected to the earthing mat. But because of high resistance of earthing mat (130 ohm on LV and 180 ohm on HV), one day LV side neutral earthing conductor melted and we had a huge damage. Can any one plz tell me what might happen when we connect power transformer neutral to the earthing mat which has high resistance (>100 ohm ) ?????
What cmos is and its benefits?
Are you connected Transformer neutral eathing with it's body earthing or earthing met of switch yard.? Yes or No ? why ?
in power station power measuring unit is KW but in transformer is KVA why?
two generator runnig with parallel but only one NGR on And one off Why
What is the end effect of linear induction motor ??
WHAT HAPPEN WHEN A DROP OF WATER MIXED UP WITH TRANSFORMER OIL ?
what is S.D.F stands for ? (S.D.F unit 80 amp , TPN )
LET ME NOW MORE ABOUT icu and ics for circuit breaker. how we calculate the rating of circuit breaker and i c u and ics values
How will I know that how many batteries I should connect to my UPS unit?
11 kv metering is done in my factory.Meter show PF 1.000 but kvarh lag&lead show 24&94 respectively & Avg.PF is .956 .? is what i do for inproove my PF to 1.000
Up to how much limit of HP of electric motor the Star- Delta Starter can be used ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)