How the real power output is controlled in a Generator?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
In case of grid connected gen ,only the prime mover can control.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / man
in grid connected alternator the active power can be
controlled by prime mover input.
if prime mover input is increased, the active power
delivered to infinite bus rises because of the increase in
load angle as E shifts away from infinite bus voltage V.
P= (E*V*sin(delta))/X
X= synchronous reactance
delta= load angle
E=excitation voltage
V= terminal voltage/ bus voltage
| Is This Answer Correct ? | 1 Yes | 0 No |
Why Neutral Isolation is required?
EXPLAIN THE TERMS "INTEREST AND DEPRECIATION" AS APPLIED TO ECONOMICS OF POWER GENERATION.
why we are discharging h.t supply during shutdown time
if voltage is not builed up in small generator what will be the reason?
A well system is when , no. of bus bar is less or more. Tell me the concept of it.
Explain in details how you would react to an unexpected incident when your supervisor or manager is not around to give instructions?
can we use 220 volt 15 w a.c. lamp on 220 volt d.c.
What is an ac motor?
how to calculate relay rating for 50kw load
Using 11000V/433V,3 ph,50Hz,500 KVA, what is the maximum capacity of motor in KW that can be connected and started at a single moment? Also explain about any calculations and formulas used in deriving the same.
What is four quadrant metering system.
how to calc. current for 5MVAR,50hz,33kv
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)