How the real power output is controlled in a Generator?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
In case of grid connected gen ,only the prime mover can control.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / man
in grid connected alternator the active power can be
controlled by prime mover input.
if prime mover input is increased, the active power
delivered to infinite bus rises because of the increase in
load angle as E shifts away from infinite bus voltage V.
P= (E*V*sin(delta))/X
X= synchronous reactance
delta= load angle
E=excitation voltage
V= terminal voltage/ bus voltage
Is This Answer Correct ? | 1 Yes | 0 No |
i am getting to neutral earth voltage zero ,is this a perfect earthing ?
how does a submersible pump work..?
why transmission voltage is 230kv and not 220kv which is a multiple of 11
1 Answers Mettur Thermal Power Station, Siemens,
What are books to be referred for KPTCL exam?
why we use negative feedback in control system.
What is the formula to calculate the rating of a three phase trnasformer
What type interview questions ask in Electrical technicians
Motor and transformer working with same principle so why motor rotates while transformer not?
What is system earthing?what are the types?
what is the method to calculate the voltage drop for number of meters Example 250volts I/p at one end if the cable length is 50 meters what could be the drop?, after 100 meters how much? needs formulae.
in a large three phase induction motors usually the value of full load slip is
I WANT TO INSTALL LIGHTING ARRESTOR ABOVE 20 FEET HEIGHT INDUSTRIAL BUILDING. NOW IT WAS 15 FEET HEIGHT HOW MUCH DISTANCE IT WILL COVER & HOW TO CALCULAT THE DISTANCE COVER BY THE ARRESTOR