Why the meters sonnected to metering core of CT are not
damagedon event of a fault??? Explain the phenomena??
The iron core of metering CT is smaller compared to that of
protection scheme, for accuracy. Its core reaches magnetic
saturation , if the current exceeds the rated value by a
certain value. After the saturation is reached, the
secondary current wii not incease with the primary
current .
Is This Answer Correct ? | 3 Yes | 0 No |
Does outdoor isolator loose connection cause short circuit current in that circuit? if yes then how ??
Is it necessary to carry out sheath test after cable jointing? If the value is zero of such instance , is it ok to energize the cable?
How many no of flip-flops are required to get 16 bit counter
I have 2 transformers in two different plants, both are without OLTC but i am facing problem of voltage fluctuation at LV side from only one transformer. i have to change its taps manually twice in a day. Another transformer delivering voltage is ok. Please guide me about the problem
What happen if we re-start H.T motor whose rotor is running at 40% rated speed. Is it will damage motor winding?
what happen if the parallel generator phase angle shift by 1 degree in manual mode
whether starting current is limited to rated current of motor through soft starting or it exceeds the rated current?
What will happen to the speed of synchronous machine subjected beyond the pull out torque? Are the behavior shown by rotor remains same for both the alternator and motor?
Why neutral is used in electrical system?
How to calculate the current in DG What are the type of power pls explain with related formulas
1 Answers Corona Enterprises, Sodexo,
difference between high and low impedance BUS BAR relay??
what is a composite error in current transformers, why occurs & in which it will occur i.e, either metering ct/ protection ct