how we can select a transformer based on a particular load.
suppose we have 4 motors of rating 40 h.p , 50 h.p, 80 h.p
& 100 h.p. then what rating of transformer we can select.
urgent. pls reply
Answers were Sorted based on User's Feedback
Answer / mayank goel
40+50+80+100
=270HP
1 HP=746Watt
270HP=201.42KW
Power Factor@.7=287KVA
Loading on Transformer 85%=337KVA
So we can use 400KVA transformer for this motors is okey.
| Is This Answer Correct ? | 23 Yes | 0 No |
Answer / eng. ahmed esmail
total HP = 40 + 50+80+100=270HP
1HP=0.746KW
total Kw =201.42Kw
at 0.75 power factor
P= S *P.F
S=268.56 KVA
at 0.85 transformer loading
S=268.56/.85=315.95 KVA
so we will use 400 KVA transformer for this motor loads
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / rahul
=40+50+80+100
=270HP
1 HP=746Watt
270HP=201.42KW
So we can use 250KVA transformer for this motors.
| Is This Answer Correct ? | 18 Yes | 10 No |
Answer / ramesh behera
Here the g0hpiven motor values are
40HP,50HP,80HP,100HP
so total HP of motors are
40+50+80+100=270hp
1hp = 746watt
so 270*746=201420w
or 201.42kw
201.42*.85=251.744kva
Some power in hand so we should use 260kva single phase
transformer for these motor load
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / suber
approxmatle 300kva tfr futter add and the load so 333kva
the ans
| Is This Answer Correct ? | 4 Yes | 11 No |
Answer / jitesh
=40+50+80+100
=270kva
=362 kw
=270+(270*50%)
=400approx = 500kva X'mer
| Is This Answer Correct ? | 3 Yes | 15 No |
if there are six generators (3 gas CATT, one Jenbacher o1 MW each, and two nos Diesel 01 no 01 mw other 0.65mw EDGs ( say), 3 CAtt gas set have identical pole pitch,01mw EDG and Jenbacher gas Set have different pole pitch, how their power connection can be done to connect a common bus bar during installation. in short, how different pole pitched generators power connection can be done to connect a common busbar system through generators incomer ACBs.
What are the advantages of vscf wind electrical system?
Is it possible to measure correct value of earth resistance & cable insulation ristance with out disconncting earth lead & both sides of cable ends? If not, any other method to measure ER & CIR with out disconneting from the system.
What is MPCB, MCCB, ELCB, RCCB ? Explain them ?
Why there is no provision of breaker in between primary of UAT and generator
What type of tranformer generaly at soft wares like capacity 2000 kva 1800 kva etc iam confused it CT or PT OR distribution tranformer
what is meant by negative conductor?
HOW to speed control of induction mototr using scalar control
what is the operation of regulator in fan?
which safety we have to take when we go for work?
how a generating station can monitor its multi users power factor. What type of incentive /penalty is associated with power factor management.
What is STEP VOLTAGE ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)