how we can select a transformer based on a particular load.
suppose we have 4 motors of rating 40 h.p , 50 h.p, 80 h.p
& 100 h.p. then what rating of transformer we can select.
urgent. pls reply
Answers were Sorted based on User's Feedback
Answer / mayank goel
40+50+80+100
=270HP
1 HP=746Watt
270HP=201.42KW
Power Factor@.7=287KVA
Loading on Transformer 85%=337KVA
So we can use 400KVA transformer for this motors is okey.
| Is This Answer Correct ? | 23 Yes | 0 No |
Answer / eng. ahmed esmail
total HP = 40 + 50+80+100=270HP
1HP=0.746KW
total Kw =201.42Kw
at 0.75 power factor
P= S *P.F
S=268.56 KVA
at 0.85 transformer loading
S=268.56/.85=315.95 KVA
so we will use 400 KVA transformer for this motor loads
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / rahul
=40+50+80+100
=270HP
1 HP=746Watt
270HP=201.42KW
So we can use 250KVA transformer for this motors.
| Is This Answer Correct ? | 18 Yes | 10 No |
Answer / ramesh behera
Here the g0hpiven motor values are
40HP,50HP,80HP,100HP
so total HP of motors are
40+50+80+100=270hp
1hp = 746watt
so 270*746=201420w
or 201.42kw
201.42*.85=251.744kva
Some power in hand so we should use 260kva single phase
transformer for these motor load
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / suber
approxmatle 300kva tfr futter add and the load so 333kva
the ans
| Is This Answer Correct ? | 4 Yes | 11 No |
Answer / jitesh
=40+50+80+100
=270kva
=362 kw
=270+(270*50%)
=400approx = 500kva X'mer
| Is This Answer Correct ? | 3 Yes | 15 No |
How can step up and step down process in power transformer
1 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
what will happen at secondary side of transformer if i increase voltage at primary side?while V1*I1=V2*I2 will secondary voltage or current increase?
One of the advantages of HRC fuse links is that they can be used to back up equipment with an inadequate rupture rating. briefly discuss what this means
please can i know about total harmonic distortion and how i can calculate it and if anyone can help me to find any program to help me to calculate THD?? please need it
What will happen when more than one star neutral points at same voltage level are connected to earth by metallic conductor?
what is leading power?
what is the difference between brushed alternator ,brushless alternator & permanent alternator ?
What is the alternate solution for testing of polarity by using polarity tester while its milli ammeter does not works?
How to connect the chemical earthing and complete process tell me plz
what's the reson that,Load is not same on VFD I/P and O/P Side.whenever DOL condition load is same I/P and O/P side.
what is the diffrence between kav and kvar?
while doing high voltage test on 11kv/433 distribution transformer why we only give 28 kv on hv side and 3kv on lv side for power transformers what is the value what factors it depends
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)