Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how we can select a transformer based on a particular load.
suppose we have 4 motors of rating 40 h.p , 50 h.p, 80 h.p
& 100 h.p. then what rating of transformer we can select.
urgent. pls reply

Answers were Sorted based on User's Feedback



how we can select a transformer based on a particular load. suppose we have 4 motors of rating 40 ..

Answer / mayank goel

40+50+80+100
=270HP
1 HP=746Watt
270HP=201.42KW
Power Factor@.7=287KVA
Loading on Transformer 85%=337KVA

So we can use 400KVA transformer for this motors is okey.

Is This Answer Correct ?    23 Yes 0 No

how we can select a transformer based on a particular load. suppose we have 4 motors of rating 40 ..

Answer / eng. ahmed esmail

total HP = 40 + 50+80+100=270HP
1HP=0.746KW
total Kw =201.42Kw
at 0.75 power factor
P= S *P.F
S=268.56 KVA
at 0.85 transformer loading
S=268.56/.85=315.95 KVA
so we will use 400 KVA transformer for this motor loads

Is This Answer Correct ?    12 Yes 2 No

how we can select a transformer based on a particular load. suppose we have 4 motors of rating 40 ..

Answer / rahul

=40+50+80+100
=270HP
1 HP=746Watt
270HP=201.42KW
So we can use 250KVA transformer for this motors.

Is This Answer Correct ?    18 Yes 10 No

how we can select a transformer based on a particular load. suppose we have 4 motors of rating 40 ..

Answer / ramesh behera

Here the g0hpiven motor values are
40HP,50HP,80HP,100HP
so total HP of motors are
40+50+80+100=270hp

1hp = 746watt
so 270*746=201420w
or 201.42kw

201.42*.85=251.744kva

Some power in hand so we should use 260kva single phase
transformer for these motor load

Is This Answer Correct ?    4 Yes 3 No

how we can select a transformer based on a particular load. suppose we have 4 motors of rating 40 ..

Answer / suber

approxmatle 300kva tfr futter add and the load so 333kva
the ans

Is This Answer Correct ?    4 Yes 11 No

how we can select a transformer based on a particular load. suppose we have 4 motors of rating 40 ..

Answer / jitesh

=40+50+80+100
=270kva
=362 kw
=270+(270*50%)
=400approx = 500kva X'mer

Is This Answer Correct ?    3 Yes 15 No

Post New Answer

More Electrical Engineering Interview Questions

how the ac voltage are selected like 220v,415v,750v,1000v& 1.KV,6.6KV,11KV,33KV,66KV,132KV,220KV & why these are selected like these orders

2 Answers   Jindal, JSW,


whay is snubber circuit , why we are using snubber circuit in thyristor

1 Answers   NEPC,


if u want to buy a motor than what will be the configuration of that motor?

2 Answers  


how to test reverse power trip?

0 Answers  


Dear all, is ther any body who can tell me about the setting of ACB(air circuit breaker ). what kind of it,s setting is and how to do it,s setting. also please tell me the setting of VCB(vaccume circuit breaker) . please tell me their setting,s. i will b very thank ful to all of u. Thank,s and Regard,s. Muhammed Ikram.

2 Answers  


If the (Motor control center)Panel work on field the relay used in panel in the case this will be damage and no indication provide on panel.fault occur in panel and MCB will not trip. how happen the relay damage in panel and what effect of panel.

1 Answers  


mcb kitna type ka hata hai aur uska pura naam please bataye

2 Answers  


Give accurate definitions for these electric terms: Inductor Inductance Inductive Induction Reactance Reactive Esam Baraka ٢١ ساعة

0 Answers   HMK,


1. what is exciting winding, rotor winding, startor winding. and how it works? in ac generator

3 Answers  


can i connect REF and Differencial relay in 1 CT core for transformer protection?

0 Answers  


Why donot sleep below the tree for night time?

12 Answers  


How much must be gape bitween 2 cable on cable tray?

1 Answers   El Seif,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)