how we can select a transformer based on a particular load.
suppose we have 4 motors of rating 40 h.p , 50 h.p, 80 h.p
& 100 h.p. then what rating of transformer we can select.
urgent. pls reply
Answers were Sorted based on User's Feedback
Answer / mayank goel
40+50+80+100
=270HP
1 HP=746Watt
270HP=201.42KW
Power Factor@.7=287KVA
Loading on Transformer 85%=337KVA
So we can use 400KVA transformer for this motors is okey.
Is This Answer Correct ? | 23 Yes | 0 No |
Answer / eng. ahmed esmail
total HP = 40 + 50+80+100=270HP
1HP=0.746KW
total Kw =201.42Kw
at 0.75 power factor
P= S *P.F
S=268.56 KVA
at 0.85 transformer loading
S=268.56/.85=315.95 KVA
so we will use 400 KVA transformer for this motor loads
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / rahul
=40+50+80+100
=270HP
1 HP=746Watt
270HP=201.42KW
So we can use 250KVA transformer for this motors.
Is This Answer Correct ? | 18 Yes | 10 No |
Answer / ramesh behera
Here the g0hpiven motor values are
40HP,50HP,80HP,100HP
so total HP of motors are
40+50+80+100=270hp
1hp = 746watt
so 270*746=201420w
or 201.42kw
201.42*.85=251.744kva
Some power in hand so we should use 260kva single phase
transformer for these motor load
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / suber
approxmatle 300kva tfr futter add and the load so 333kva
the ans
Is This Answer Correct ? | 4 Yes | 11 No |
Answer / jitesh
=40+50+80+100
=270kva
=362 kw
=270+(270*50%)
=400approx = 500kva X'mer
Is This Answer Correct ? | 3 Yes | 15 No |
What is the restart inhabit setting in ABB spam150c relay (Motor protection relay)
what is ten delta test? what is the significanse of it
What happen if an alternator rotates in reverse direction?
6.6Kv feeder feeding tow step down transformers-415V-,what the possible consideration for parrellel operation?
regarding safety what would u consider the most important rules to observe when inspecting electrical equipment?
0 Answers Reliance, Southco Utility,
How wire size can define in electrical wiring? What is the ratio?
how electronic energy meter works?
which type of insulation are used on 132kv transmission line
If I have 3 essential main switch board and 3 incoming electricity ,but only 1 genset running is that possible.
What is delta stare switch?
1.Can anybody explain Why starters are not used for motor starting in industries? 2.
what will happen when reverse reactive power occurs in alternators?