how we can select a transformer based on a particular load.
suppose we have 4 motors of rating 40 h.p , 50 h.p, 80 h.p
& 100 h.p. then what rating of transformer we can select.
urgent. pls reply
Answer Posted / ramesh behera
Here the g0hpiven motor values are
40HP,50HP,80HP,100HP
so total HP of motors are
40+50+80+100=270hp
1hp = 746watt
so 270*746=201420w
or 201.42kw
201.42*.85=251.744kva
Some power in hand so we should use 260kva single phase
transformer for these motor load
Is This Answer Correct ? | 4 Yes | 3 No |
Post New Answer View All Answers
What is core CT & it's function?
List the advantages of star-delta starter with induction motor?
what are the stresses in circuit breakers ?
what about GD square and its important for motor design?
can mini-curcuit supply MIL-tested transformer !
what is a pulse transformer? how rise time of pulse changes when ever the voltage changes?
hi, in the event earth grounding is not available in a project, is there any other way to make the elcb work? fyi, i have an instant water heater (6.5kw) installed, however if there is grounding in the heating element inside the heater assembly, i will get grounded. thank you in advance to those who will answer my question.
how much maximum load a 2 core (Single phase) 16mm aluminium wire can take ?
What is the function of auadag in a cro?
how could we calculate the no of outgoings from a 800 watt distribution board
what percent do you derate your copper wire when you change from copper buss to copper wire
What are the types of excitation system?
What is the method of estamating of cable, CB,MCB ?
How can we calculate the motor frame sizes?
difference between Ac and Dc mcb ????