how we can select a transformer based on a particular load.
suppose we have 4 motors of rating 40 h.p , 50 h.p, 80 h.p
& 100 h.p. then what rating of transformer we can select.
urgent. pls reply

Answer Posted / ramesh behera

Here the g0hpiven motor values are
40HP,50HP,80HP,100HP
so total HP of motors are
40+50+80+100=270hp

1hp = 746watt
so 270*746=201420w
or 201.42kw

201.42*.85=251.744kva

Some power in hand so we should use 260kva single phase
transformer for these motor load

Is This Answer Correct ?    4 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is core CT & it's function?

1634


List the advantages of star-delta starter with induction motor?

618


what are the stresses in circuit breakers ?

1524


what about GD square and its important for motor design?

3294


can mini-curcuit supply MIL-tested transformer !

1627






what is a pulse transformer? how rise time of pulse changes when ever the voltage changes?

1492


hi, in the event earth grounding is not available in a project, is there any other way to make the elcb work? fyi, i have an instant water heater (6.5kw) installed, however if there is grounding in the heating element inside the heater assembly, i will get grounded. thank you in advance to those who will answer my question.

1522


how much maximum load a 2 core (Single phase) 16mm aluminium wire can take ?

2194


What is the function of auadag in a cro?

684


how could we calculate the no of outgoings from a 800 watt distribution board

1263


what percent do you derate your copper wire when you change from copper buss to copper wire

1555


What are the types of excitation system?

1482


What is the method of estamating of cable, CB,MCB ?

1680


How can we calculate the motor frame sizes?

2919


difference between Ac and Dc mcb ????

1137