Hi All,
I am working as a Technical executive in a MNC company and
we have 1500KVA & 1250KVA T/F in our site, can you help me
that how many maintenance tests can be conducted and what
are the procedures included for the tests can you share
yours answers and also give any web address to get more
information on this
Answers were Sorted based on User's Feedback
Dear friend ,
Transformer is a heart of the electrical system & that is
the reason it required more care.
Daily :-
Check the Oil level in Conservator.
check for any leakage in transformer
Check for any abnormal sound
check for Colour of silica gel.
Check for any air in Bucholz realay , if found realease
with the air vent provided in the relay.
Yearly.
Check the Dielectrica strengh of oil , filter it & if
required replace it.
Check the earthing value of a Earthpit if required topup
with salt & water.
Check the tighness of the connection both the way Primaty
side & secondary side.
Clean the transformer yard throughly.
If required lay the granuals in the transformer yard.
By proper shut down manually check the tripping point of HT
breaker tripping set points like ( OT, WT & Bucholz Relay )
check the secondary side voltage as per desired voltage &
if any missallign found adjust with the tap changer.
please revert if any quarry exists.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / tariq
in onload u cant do any test except temprature and sudden
pressur or oil level in conservator.oil leakage,cileco gel
colore for moisture,but in offload u can some more test
also.if u send ur question in detail may b i can help u
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / thyagarajan
checking of oil level in seal
reconditioning of silica gel
cleaning the bushing
check temp alarm
meger
check oil level in oltc, conservator
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dr reddy's corporate offi
hai
1)take first permission from client & hod
2)switched off the brekers
3)rack out brekers applied loto kit
4)chek primary winding bushes & secondry winding bushes
5)chek silcazel colour(breather)
6)chek oil level & density of oil(resistance)
7)primary winding , secondary winding & core bolts retigtend
8)warnish apply winding
9)take break down votage test
10)chek oil teperature & winding temperaure guages functiong
11)chek oltc counter daily basis
12)trail tests taken buchloz realy
Is This Answer Correct ? | 0 Yes | 0 No |
advantages & disadvantages of Lagging and leading power factor .
how to calculate circuit breaker capacity
why the star delta motors burn out frequently
Why Humming noise originated in Starter motor and how it was generated ?
could you measure current in parallel?
what is back trip and re-trip in protection schemes? why these two? define me the exact function of these two?
How do you select the pickup value of the relay?
why efficiency of generator is greater than motor?
Is there any reason that we get shock on touching phase wire because the earth is at neutral potential? Is there any reason that the earth is at neutral potential because the neutral is earthed in apower station
How to calculate % Impedence?
1 KW = how many kva
what is the speed of current?