Hi All,

I am working as a Technical executive in a MNC company and
we have 1500KVA & 1250KVA T/F in our site, can you help me
that how many maintenance tests can be conducted and what
are the procedures included for the tests can you share
yours answers and also give any web address to get more
information on this

Answers were Sorted based on User's Feedback



Hi All, I am working as a Technical executive in a MNC company and we have 1500KVA & 1250KV..

Answer / virendra joshi

Dear friend ,

Transformer is a heart of the electrical system & that is
the reason it required more care.

Daily :-

Check the Oil level in Conservator.
check for any leakage in transformer
Check for any abnormal sound
check for Colour of silica gel.
Check for any air in Bucholz realay , if found realease
with the air vent provided in the relay.

Yearly.

Check the Dielectrica strengh of oil , filter it & if
required replace it.

Check the earthing value of a Earthpit if required topup
with salt & water.

Check the tighness of the connection both the way Primaty
side & secondary side.

Clean the transformer yard throughly.

If required lay the granuals in the transformer yard.

By proper shut down manually check the tripping point of HT
breaker tripping set points like ( OT, WT & Bucholz Relay )

check the secondary side voltage as per desired voltage &
if any missallign found adjust with the tap changer.


please revert if any quarry exists.

Is This Answer Correct ?    3 Yes 0 No

Hi All, I am working as a Technical executive in a MNC company and we have 1500KVA & 1250KV..

Answer / tariq

in onload u cant do any test except temprature and sudden
pressur or oil level in conservator.oil leakage,cileco gel
colore for moisture,but in offload u can some more test
also.if u send ur question in detail may b i can help u

Is This Answer Correct ?    3 Yes 1 No

Hi All, I am working as a Technical executive in a MNC company and we have 1500KVA & 1250KV..

Answer / shivakumar.s

Which type of T/F ? Tell me first.

Is This Answer Correct ?    3 Yes 2 No

Hi All, I am working as a Technical executive in a MNC company and we have 1500KVA & 1250KV..

Answer / thyagarajan

checking of oil level in seal
reconditioning of silica gel
cleaning the bushing
check temp alarm
meger
check oil level in oltc, conservator

Is This Answer Correct ?    1 Yes 0 No

Hi All, I am working as a Technical executive in a MNC company and we have 1500KVA & 1250KV..

Answer / dr reddy's corporate offi

hai
1)take first permission from client & hod
2)switched off the brekers
3)rack out brekers applied loto kit
4)chek primary winding bushes & secondry winding bushes
5)chek silcazel colour(breather)
6)chek oil level & density of oil(resistance)
7)primary winding , secondary winding & core bolts retigtend
8)warnish apply winding
9)take break down votage test
10)chek oil teperature & winding temperaure guages functiong
11)chek oltc counter daily basis
12)trail tests taken buchloz realy

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

How to connect a Restricted earth fault relay for 2000KVA,11/0.433 KV Distribution Transformer and What is the neutral CT ratio should be selelcted for 2000 MVA Transformer for estabilishing the Restricted earth fault relay

1 Answers  


What is meant by Active and reactive power?

5 Answers   Siemens,


how many type of of electrical fuse please explan?

9 Answers  


what is d meaning of inrush current of a trafo ? how u can calculate this ?

1 Answers   Jindal,


In my project i am layout cables under the Maintainance bay /Maintainance yard in the TG Building. Whether in this route i can lay the H.T.Cables??? i am taking all H.T cables from the H.T Transformer to the TG Building..

1 Answers  






what is W.T?specify the acceptable range?

0 Answers  


What is the multiplying factor if line ct ratio is 1000/1 and meter ct ratio is -/5 ?

1 Answers  


after parallaing two generators current is shooting up in both the generators.for ex: load is 400 kw..after paralling and load sharing current in running gen is approx 900 amps and incoming is 750 amps which is too high when trying toshift the load current in incoming gen is coming more than 1300 amps and both getting tripped and making blackout..

3 Answers  


what is a types of short circuit and what is a types of distance protection tests

0 Answers   Anna University,


What is the Surge suppresor? Why using in a UDB's and How it works?

0 Answers  


what is the terminal voltage of dc series generator running at rated speed at no load?

2 Answers  


Is it posssible to obtain the higher speed(3000rpm) for adiferentiallly cascaded induction motors(with 8 and 6 poles)

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)