Answer / nihar ranjan mandal
Amount of vacuum required to quench the arc at 132 KV level
will be very high. It is difficult to maintain that amount
of vacuum in practical purpose. Now a days we use GIS( gas
insulated substation for 132KV level. Where arc is quenched
in hydrogen chamber.
| Is This Answer Correct ? | 15 Yes | 1 No |
Answer / karunakar
Ionisation at higher voltages causes arcing between breaker
contacts hence deteoriation of contactors. This raises
another methods for arc quenching.. so for medium voltages
currents upto 3000A VCB's have longer life and better
operability.
| Is This Answer Correct ? | 7 Yes | 2 No |
Degree of Vacuum required for quenching of ARC at 132 kV
level system fault is very high and its very difficult to
maintain that much degree of Vacuum so don't use VCB in 132
kV level. we generally used SF6 for this purpose.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / jobmon jacob
Factors contributing to interuptor selection are 1)voltage
2)metallurgy 3)vacuum 4)size 5)sc rating6)current chopping etc.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raghu
In 132kv and above switch gear required very high vacuum to quenching arc during making/breaking the contacts, now a days we r using gas insulated and sf6 switch gears for proper operation.
| Is This Answer Correct ? | 0 Yes | 0 No |
What are the basic components of the feedback control system?
I have 30 kw motor load & i have selected 10 kvar capacitor bank for power factor improvement.my existing p.f is 0.85 & proposed p.f is 0.99 so ,is it right selection? 2 nd question how to connect c.bank whether in delta or star connection & how to decide it?
why is only third harmonics is dangerous for electrical equipments?
How to calculate cable size by using load.?? Any formula...
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
what is the difference between KW and KWh?
why the neutral of power transformer is always earthed?
How select ELCB for 32amp. socket having quantity 12Nos. We have to do this wiring in PLANT. Please Also explain the incoming cable specification.
0 Answers Gulf Industrial Services Company GISCO,
What do you mean by a current transformer?
In a overhead system why the voltage between line &ground is taken for basic comparison ?and in case of underground cables the comparison take only by the voltage between cables?
What kind of preventive maintenance are there for AC generator?
What does ampere turns shows?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)