Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

why VCB are not used in 132KV system(above 33KV system)

Answer Posted / karunakar

Ionisation at higher voltages causes arcing between breaker
contacts hence deteoriation of contactors. This raises
another methods for arc quenching.. so for medium voltages
currents upto 3000A VCB's have longer life and better
operability.

Is This Answer Correct ?    7 Yes 2 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Installation resistance for whole installation of 16 kva & 25 KVA DTRA a) Between each conductor b) between conductor to earth c) installation resistance for each apparatus, each conductor to earth d) earth resistance for the system of earthing

1934


I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?

1891


Post possible questions for Power Factor Panel FAT / SAT

1409


What is the minimum IR value of HT/ LT cable? Pls post separetely!!!!!

2452


what is the operating time for LBB and how does the LBB relay realise whether cb is opened or not?

1988


State the other types of Air Conditioners?

2067


Greeting to all members, How to calculate spill current when we have different ratio CT and Class for REF(Low Imp) I have 500/1A 5P20 @line side n 400/1A CL.X @ Neutral.

3010


How to calculate per unit impedance of transformer?

2211


in star-delta tranformer,if the input of star connection is 400/7v 3 kva then what is the output of delta connection?

2134


plz send me HPCL apptitude paper.. maulik_elect@yahoo.co.in

2091


What is difference between YNyn0 and YNyn ??

2563


while doing high potential for 11KV 3 core cable how much leakage current will obtain?, what will be acceptance value?

2887


what topics we have to concentrate for power grid et.written test.and tell what to read for english synonyms and antonyms.

1956


how to calculate the mesh earth network resistance in such substation, is there any recommended resistance values with references , thanks!

2341


Which do you think is the most significant cause of energy loss in a factory?

2248