Why we use 4 to 20 mA, (This is International Standard)
instaed of this can we use 4-16, or 4-24 or 3- 15 or any
other range
Answers were Sorted based on User's Feedback
Answer / nagarajan.p
First the question is why can't we use 3~15mA or other
range, here also we can check live zero and also we can go
step current like 3,6,9,12,15(i.e 0%,25%,50%,75%,100%).ok
The reason is the transmitter voltage is 24Vdc , here we
can load max of 600 ohms, for this voltage & load better
range is 4~20.
Why 4 ~ 20 is better since we can convert easily 1~5Vdc by
put 250 ohms.All the controllers and DCS , PLCs are operated
by the input of 1~5Vdc (external or Internal convertion)
Is This Answer Correct ? | 47 Yes | 5 No |
Answer / nilesh upadhyay
There are basically 2 reasons of using 4-20ma
1. we can know whether the instrument is working properly
or not. we can distinguish "live zero" and "dead band". if
there is problem in instrument then also it is going to
show zero and if there is no supply then also it will show
zero so we can differentiate this two.
2. 4-20ma is linear with 3-15psi .
Nilesh Upadhyay...
Is This Answer Correct ? | 23 Yes | 12 No |
Answer / richard marks
the 4mA zero is termed a "live zero". If 0mA was the zero
point there would be no way of telling if the transducer
was reading zero or in a fault condition eg. an open loop.
with a 4mA zero an open loop would drive the indicator eg.
a recorder into a minus figure (-25%). The 4 - 20mA scale
is to give a calibration points for 0-25-50-75-100%.
Because the start point is 4 the steps are 4mA.
Is This Answer Correct ? | 14 Yes | 6 No |
Answers 5 & 6 are totally correct.. just adding another point.
20 mA as upper value is used to keep electrical components
intrinsically safe at hazardous area.
Is This Answer Correct ? | 8 Yes | 3 No |
Answer / dhaval joshi
for any active ckt make it standard 1 volt dc
actually formula is 20-4= 16 then
16/1000*250=4 ma
32/1000*250=8 ma
48/1000*250=12 ma
64/1000*250=16 ma
80/1000*250=20 ma
by using 250 ohm resistance and standard 1000 ma it give
standard voltage.
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / rajesh.a
STANDARD VOLTAGE IS 1-5V DC,250OHM RESISTANCE
AT V=I*R
AT 1V=I*250OHM = 4MA
AT 5V=I*250 OHM = 20MA
SIMPLE CALCULATION
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / anup ramteke
Answers 5, 6 & 7 are correct. just want 2 add that why cant
we use 3 mA current as lower value. The reason is that there
are many small noise signals that can be picked up by our
signal wire which has the potential of providing upto 3 mA
current. So to be on the safe side to distinguish between
our proper field signal and the noise pick-ups we use 4 mA
as our lower value
Is This Answer Correct ? | 6 Yes | 5 No |
Answer / abdus sattar mollah
ALL ANSWERS ARE WRONG.....
4-20 is a standard because transistor which is the basic building block of any transmitter has a linear output charecteristics in 4-20ma range.
Is This Answer Correct ? | 4 Yes | 8 No |
Answer / mayur
ans. 5,6,7 & 8 r correct.only two points add.
1.in ancient time,niddle type galvanometers are used,only if
we pass 4mA current it shows deflection.therefore 4mA.
2.if 21mA current will pass through our body,man can goes
dead.therefore 20mA. & 4-20 mA can divided into 5 equal %.
Is This Answer Correct ? | 4 Yes | 12 No |
What is the function of SMPS
Why not come out analog output in ABB EL3020 when display show correct value
How much voltage we get between two wire of 4 to 20 ma output? Is this voltage up or down respectvice to 4 - 20 ma ?
Hi at present i m wrking with tire industry as a manager having gud ctc. Nw I am selected for 1 of the best chemical industry but my ctc is lower than current n also i hv 2 compromize vit post as post is also lower. I hv 6 yrs of exp in various type of industry. Should i join chemical industry as there ar lot of gud instrument than tire? Financialy i can manage 4 more 2 yrs. Bt during wrking vit tire industry i found there is very less instrument n feel that opportunity is less. Pl ans quickly. I have less time to decide.
How to work togather like sov,limit switch,proxy switch and booster in xv
why the steam drum and deaerator level transmitter range is in negative MMWC to zero
3 Answers Emerson, Jindal, JKPM,
How to force the bit in GE Mark V?
what is plc?
27 Answers HPCL, KRL, Noor Company, Petrochemicals, SS Automation,
If you SOURCE your outputs from a PLC, would you have to make the output HIGH, or LOW, in order to switch an output ON?
kindly tell where orifice,nozzle,air foil,ventury used in flow measurement?
what is INSTRUMENTATION ? specify..
whats the working of principal thermocouple