one rtd sensor which is connected at middle of distillation
column where actual temp. is 100deg but when we tight this
sensor at thermowell end it goes down to 90 deg & when
remove from the thermowell(but sensor end dipped in well)
showing actual reading, what is reason?
Answers were Sorted based on User's Feedback
Answer / ashwin jain
when the RTD is loose, the RTD probe direct contact to
thermowell body so RTD giving the temp.(100 deg) but when
we tighten with thermowell there is sum gap or space
between thermowell body & probe,so temp down to 90 deg.
also check the OD of thermowell.
OD of thermowell > RTD
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / nitin
i want again clear my question that, rtd showing 100 deg temp. & it is ok, but as soon as i tight the length adjustment screw that is on rtd rod to the thermo well, temp. suddenly dropped down to 90 deg, what's reason
and again i untightened that screw and kept apart from thermo well, It again showing the correct reading. what's reason
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ashok
The Question is not clear bez always temperature needs time
to reach the actual value like 100deg. so when you take out
of it will not loose the temperature until we take the senor
out.
Is This Answer Correct ? | 1 Yes | 1 No |
difference between transducer and converter in instrumentation
what's the minimum level required of SIL (safety integrity level)to use fire and gas system?
what is electric motorised valve working principle.
How to calibration coriolis flow meter?
please help me to get the below mentioned quires,which i have to submit for my client.[INSPECTION TEST PLAN] 1]I.T.P for Calibration of all instrument. 2]I.T.P for SS tubing. 3]I.T.P for Fire & Gas devices. 4]I.T.P for CCTV & telecommunication. 5] I.T.P for loop checking.
Somebody ask me how many size of control valve what is mean of control valve size?
WHEN BOTH WIRES OF THERMOCOUPLE R SHORTED WHAT IS THE OUTPUT THE TEMP ARE 0,30,250,320
how is a displacer type level transmitter calibrated.explain the method?
why does mA signal preferred for signal transmission?
In turbine, what does term CDP, NI, NH, HSSOC, means
ABB DCS (AC 800 M)redundency take howmany milliseconds to switch from master controller to slave?should be less than DCS scanning time?
What is force balance principle?