what is the working principle of soft-starter & how it
diff. from VFD ?????????
Answers were Sorted based on User's Feedback
Answer / phanindra kumar .m
A softstarter is replica of a star-delta starterin which
starting current is controlled by reducing voltage using ac
voltage controller for smooth starting.As Ac voltage
controllers are not suitable for speed control.So,soft
starters are mainly used for starting purpose only.(since
in Ac voltage controller,frequency is fixed,only voltage
has to be varied.Also,It produces predominant harmonics
into the system.
Where as by using VFD,we can control both voltage and
frequency,so speed control is possible above and below Ns.
| Is This Answer Correct ? | 43 Yes | 4 No |
Answer / ram sajeevan patel
A softstarter is replica of a star-delta starterin which
starting current is controlled by reducing voltage using ac
voltage controller for smooth starting.As Ac voltage
controllers are not suitable for speed control.So,soft
starters are mainly used for starting purpose only.(since
in Ac voltage controller,frequency is fixed,only voltage
has to be varied.Also,It produces predominant harmonics
into the system.
Where as by using VFD,we can control both voltage and
frequency,so speed control is possible above and below Ns.
| Is This Answer Correct ? | 15 Yes | 1 No |
Answer / mehul.soni
A soft starter is similury of DOL & Star-Delta starter.
A soft starter does control for starting current.
Where as by using VFD,we can control both voltage and
frequency,so speed control is possible above and below Ns.
| Is This Answer Correct ? | 15 Yes | 7 No |
Answer / jitendra pathak
A soft starter does control for starting current and VFD
does control rpm of the drives accordingly voltage setting.
| Is This Answer Correct ? | 27 Yes | 26 No |
Answer / alfred salazar
The VFD works on the principle that the AC line voltage is converted to a DC voltage. This DC voltage is then inverted back to a pulsed DC whose RMS value simulates an AC voltage. The output frequency of this AC voltage normally varies for 0 up to the AC input line frequency. On certain applications the frequency may actually go above the line frequency. Though high performance current regulated AC drives capable of
operating in “torque mode” are available, the more prevalent volts per hertz drive is addressed. While Soft-starter, For induction motors, the starting torque is approximately proportional to the square of the starting current drawn from the line. This starting current is proportional to the applied voltage. So the torque can also be considered to be approximately proportional to the applied voltage. By adjusting voltage during starting, the current drawn by the motor and the torque produced by the motor can be reduced and controlled. Operation of Soft starters, Timing of when to turn on the SCR’s is the key to controlling the voltage output of a soft starter. During the starting sequence the logic of the soft starter determines when to turn on the SCR’s. It does not turn on the SCR's at the point that the voltage goes from negative to positive, but waits for some time after that. This is known as “phasing back” the SCR's. The point that the SCR’s are turned on is set or programmed by what is called either initial torque, initial current or current limit setting.
The input voltage to the soft starter is the same as the VFD. The result of phasing back the SCR’s is a non-sinusoidal reduced voltage at the terminals of the motor. Since the motor is inductive and the current lags the voltage, the SCR stays turned on and conduct until the current goes to zero. This is after the voltage has gone negative.
| Is This Answer Correct ? | 2 Yes | 9 No |
what r the types of detectors? state the location these detectors?
How is efficiency of DG set calculated? At many places I found the efficiency to be mentioned in percentage. But at some other places I found kWH/ litres. I want to know how dimensionless percentage value is arrived at?
what is brushless generator.How does work it..??
In control room of our one plant there is a continuously the incoming power goes to PC is vary,means in stabilizer it continuously indicate from high input to low and low input to high. what is the reason and its solution.
Meter p.t. ratio= 3×230/400 , c.t.ratio = 3×1 (2) A what is m.f.
One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?
what is stiffness factor
What is the difference between 2 wires RTD's and 3 wires RTD's.Kindly explain the wiring diagram.
what is the advantages of having in-built acvvvf (without seperate inverter in the control panel)in the drive system of elevators?
Define the term factor of inertia.
what are the standard transmision voltages in india?
what is the difference between core & shell type transformer ?& where we use those transformers ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)