why transfromer rating gives in MVA Or KVA? Why not in MW
or KW?
Answers were Sorted based on User's Feedback
Answer / alpha cherian
Transformer Copper loss depends on the current drawn and
Iron loss depends on the Voltage. These are affected by the
load connected to it. While designing it is unpredictable.
Since power factor is not constant "KW" rating will be
wrong. Hence rating in kVA.
Kw rating = kVA rating x Power factor
| Is This Answer Correct ? | 18 Yes | 3 No |
Answer / blaji
loss of trasformer dependes on voltage and current only,
not the angle between them...
anythink give supply rated on KVA--Alternator-chock-trasfo.
anythink takes power termed in KW-light-bulb,load,,,
at the time of designe we do not know about load PF,that y
Alternator rated in KVA,,
but we knew pf of any motor after designe...so we can add it
Power=V*I*pf....bk_kangaonkar@yahoo.co.in
| Is This Answer Correct ? | 17 Yes | 3 No |
Answer / satish kumar , g.noida
because transformer not is self load.transformer rating
depend upon type of connecting load
(resistive/indactive/capactive).
| Is This Answer Correct ? | 19 Yes | 7 No |
Answer / satish kumar
Because transformer is not self load so that Transformer
power factor depend upon which type of connected load such
as Resistive/inductive/capactive load
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / divya makkar
because transformer have variable power factor so that it is
rated in kva and motor has constant power factor thats why
it is rated in kw
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / roushan.eee
MVA OR KVA; WE USE FOR ELECTRICAL O/P.
MW OR KW; WE USE FOR MECHANICAL O/P.
| Is This Answer Correct ? | 6 Yes | 21 No |
Draw a SLD for main panel for school having connected load of 1200kw and emergency generator 200kw.also show the increase of additional load of chiller 225kw in the lv panel indicating meter postion size of transformer ,cables and capacitor bank.
what is load despatching
Dear All, In a 400V power system, ratio of three current transformers installed incoming switchgear is 4000/1. Maximum three phases short circuit current of this system is 48kA. One CT is installed on neutral of upstream transformer (6/0.42kV, solidly earthed) for 51G protection. Would you please inform me about the correct CT ratio of this current transformer (on neutral)?? Thanks a million
What is error of a measurement?
If DG runing time neutral is disconnected what will be the effect in Engine and Electricial panel.
Our Company's Contract Demand is 110 kVA. We use 12 Capacitors each of 12.5 kVAr Capacity to maintain Power Factor of 0.99. So, what steps should we take so that our Contract demand does not exceed 110 kVA?
What is pole slipping relay? When it is operated?
How we detect the leakage current of 11 KV H.T. motors and waht is the maximim limit?
In what condition the HT fuse breakes?
. How to calculate the Short Circuit Impedance in Transformer? How to calculate the Short Circuit Impedance in Transformer?
Briefly describe your ideal job?
Why we use 2core cable for Dc motor.Can I use 3core?
5 Answers JK Paper, Maharaja Whiteline,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)