why transfromer rating gives in MVA Or KVA? Why not in MW
or KW?
Answers were Sorted based on User's Feedback
Answer / alpha cherian
Transformer Copper loss depends on the current drawn and
Iron loss depends on the Voltage. These are affected by the
load connected to it. While designing it is unpredictable.
Since power factor is not constant "KW" rating will be
wrong. Hence rating in kVA.
Kw rating = kVA rating x Power factor
| Is This Answer Correct ? | 18 Yes | 3 No |
Answer / blaji
loss of trasformer dependes on voltage and current only,
not the angle between them...
anythink give supply rated on KVA--Alternator-chock-trasfo.
anythink takes power termed in KW-light-bulb,load,,,
at the time of designe we do not know about load PF,that y
Alternator rated in KVA,,
but we knew pf of any motor after designe...so we can add it
Power=V*I*pf....bk_kangaonkar@yahoo.co.in
| Is This Answer Correct ? | 17 Yes | 3 No |
Answer / satish kumar , g.noida
because transformer not is self load.transformer rating
depend upon type of connecting load
(resistive/indactive/capactive).
| Is This Answer Correct ? | 19 Yes | 7 No |
Answer / satish kumar
Because transformer is not self load so that Transformer
power factor depend upon which type of connected load such
as Resistive/inductive/capactive load
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / divya makkar
because transformer have variable power factor so that it is
rated in kva and motor has constant power factor thats why
it is rated in kw
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / roushan.eee
MVA OR KVA; WE USE FOR ELECTRICAL O/P.
MW OR KW; WE USE FOR MECHANICAL O/P.
| Is This Answer Correct ? | 6 Yes | 21 No |
HAT IS THE EFFECT OF LOW POWER FACTOR ON THE GENERATING STATION?HOW WILL YOU IMPROVE THE LOW POWER FACTOR?
What is high frequency grounding????Applications........
which motor will u use in refinaries?
difference btw neutral and ground?
sail kaott diploma ece ke interviw me qus.kis parkar ke aate hai aur G.S me kya puchate hai kya sameedyaan me kis parkar ke qu.puchate hai
our industries ht line so power fluctation(once drop of power please rectify causes
What are the causes of eddy current losses?
for hipot test on 33kV busbar, we will test on 70 kV or 56kV, what is the acceptable leackage current?
Due to ferranti effect which power increases at the receiving end?active power or reactive power?
Neutral to earth and phase to earth voltage how much.
Could you measure voltage in series?
What is Procedure the procedure to select CT's & PT's in 66kV and above substation?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)