HAT IS THE EFFECT OF LOW POWER FACTOR ON THE GENERATING
STATION?HOW WILL YOU IMPROVE THE LOW POWER FACTOR?
power is sold in units of KWH.The capacity of the generator is
limited by the max ampere load on the alternator.So a load of
low PF will mean a high ampere .That means you can only
generate lower KWH FROM THE GENERATOR IF THE PF IS LOW BUT BY
IMPROVING THE PF YOU CAN GENERATE A HIGHER KWH. THAT MEANS IT
IS MORE PROFITABLE.
PF CAN BE IMPROVED BY CONNECTING CONDENSORS OR PF IMPROVING
SYNCHRONOUS MOTORS.