In supply RYB are mentioned. But in transformers, why they
are mentioning XYZ?
Answers were Sorted based on User's Feedback
Answer / pillay
RYB, RST, UVW, AND XYZ IS used simply to differentiate
the various terminals.
In a transformer there are actually two sets of terminals
actually you can name them both as RYB but how are you going to
differentiate from the primary and the secondary. Now we use RYB
OR RST as the primary and the secondary as XYZ OR UVW.We use
the same reasoning whenever there are two options for example the
power connections to a soft starter or the connections in a
variable frequency drive.
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / ullas
while we are mentioning about the supply system we can see
the terms RYB.
it is not a problem in mentioning the three different
phases with R Y B or U V W or X Y Z.
but one idea shall be used while identifying the three
phases. read the terminal near to neutral as R or U or X
etc.
| Is This Answer Correct ? | 3 Yes | 7 No |
Answer / masiga
In supply(end user): It is imperative to identify the
R-red,Y-yellow,B-blue which correspond to the standard color
codes for live, ground and neutral.
In transformers(transmission): The three XYZ phases have the
same electrical components/qualities, might as well name
them UVW
| Is This Answer Correct ? | 2 Yes | 7 No |
which type of ICs can be used in resonant power converter?
the resistance of wire having length X M is R OHEM if i streched the wire to dubble length what will be the resitance
Define what is difference between fuse and breaker?
Megger type of instrument is used to check??
HOW TO CALCULATE THE WIRE SIZE FOR THE GIVEN LOAD?
Why is the generator rating always in kVA and motor rating in kW?
difference b/w eath and neutral
we have two motors 1250kW,6.6kV to be coupled on the same shaft ,so please provide assistance for their synchronisation.
what is the functioning of cvt in a substation?
During the main stator winding insulation testing (phase to ground)of 11kv alternator (Lerysomer) i found 0 and resistance with multimeter and found 20 killo ohm while the power cables are connected both end (Generator & VCB). In VCB PT (Potential transformer) are connected. Please any body explain that method of insulation is correct or not? also describe of PT connections
At what condition differential relay will act in transformer and ht motor?
I have one ct of ratio 3000-2000/1 Amp its knee point voltage mentioned on name plate is 500-333/30mA-50mA at Vk/2. in secondary box there is three terminal named 1S1, 1S2, 1S3 then on which terminal obtained the knee point voltage ie 1S1-1S2 OR 1S1-1S3 & also specify the knee point voltage for the ratio 3000 from name plate.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)