what is the formular for the calculation of CT'S when
installed as part of a electrical installation so the
correct meter is used
Answers were Sorted based on User's Feedback
Answer / denzel101
Calculate the maximum current you want to measure from your
system. for example calculate the full load current of a
supply transformer. if the full load current is 200 Amps
and your meters have 1amp rating, choose the ratio of 200:1
CT.
Is This Answer Correct ? | 2 Yes | 0 No |
There is no formula for this you just choose the correct size from what is available.
usually size the ammeter the size of the circuit.example the circuit breaker is 200 amps than the ammeter would be 200amps.The CT would be 200:5 or 200:1 whatever is available so long the ammeter is also of the same rating.
Is This Answer Correct ? | 1 Yes | 2 No |
what is resistance?
what is the effect of back reactive power on the generator ?
why we not using 230kv directly why we are stepping down and then stepping up
What happened to installed high capacity conductor for smaller current rating?
Is it possible to connect a safety device in to parallel?
which phase is preferred for connecting 1 phase vt used for synchronizing OHL? WHY?
why vector group used in transformer and what effective in output
1.how to calculate energy units in our home at singe phase, 2.415V,63A wiring what will use thickness of wire
hi frenz,its aswathy.i hve aplied for the hpcl test on feb,pls send the test patern & the placement papers as soon as possible. mail-id :kjaswathy@gmail.com
what is reactive power?, why its measured in VA ? is it transient behavior of system?
What are the protections to be used for Generator?
hi all, can any one tell me a website or document on basic interview questions on plc for a fresh diploma candidate?