1.how to calculate energy units in our home at singe phase,
2.415V,63A wiring what will use thickness of wire
Answers were Sorted based on User's Feedback
Answer / m.radhakrishnan
Energy=power *Time
Power=V*I*POWER FACTOR
how many hours consume that power, Example: 60 watts lamp
consume power in 20 hours. Energy=60*20=1200 watts hour=1.2
kilo watt hour=1.2 unit
| Is This Answer Correct ? | 3 Yes | 0 No |
What are the reasons for the parallel operation of transformers?
how to calculate the fault in substation
what is diff b/w electrical & electronics ?
Why Utility Distribution System in India is mainly at 11 kV? Why not Utility go for 33 kV?
How to calculate CT ratio for 11KV 1500KVA Transformer 500KVA MD and 1400KVA connected load ? Note:- As per MSEB(Maharastra state electricity Board)
Can we use BS 6651 and BS EN 62305 standards for computer room lightning ptotection in substation?
What does a Bode plot tell you?
If current flows through conductor it produce magnetic field only.but if current flows through vaccum both magnetic & electrical field produce why ?
why normally Generator rating are between 11Kv to 22Kv?
Is there any Institution (Not AMIE)for giving B-Tech/M-tech in Electrical engineering for those who r in service? Give the details please.
what is the maximum load sutiable from earth to phase and what is the max voltage earth to phase suitable
substation+ plc system
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)