Answer / ankit saxena
An isolation trx is a static trx, but the only difference
is that, in isolation trx both the primary and secondary
windings earthings are kept isolated from each other, so
that, there is no chance of enter any kind of harmonics in
the secondary winding supply,from the primary side or
supply side,thus it is used mostly in the UPS popurly now a
days.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / vinoth
fully isolate the entire supply... isolation done by
manually... it is diffrent from the
| Is This Answer Correct ? | 0 Yes | 2 No |
WHAT HAPPEN WHEN CT SECONDARY OPEN DURING LOAD
WHAT IS LINE TRAP,HOW IS IT FUNCTION?
what is the difference between ac motor and dc generator
What is water cooled chiller plant?
Among the following Which is vector quantity? a. Flux b. permitivity c. flux density d. magnetic intensity
We have a couple of oil tanks at our plant. One of them does not have a lightning arrester installed. My question is it necessary to install an arrestor on every tank or will this particular one be covered by the arrestor installed on the ajdacent tank, Since all the tanks are close to each other. Basically, I want to know that if these arrestors or protection works in a parituclar area of effect or influence. Thanks
I am working as a software engineer for the past 4 years. I am interested to do M.tech in premier inst. like IIT, IIIT, NIT,... I am preparing for the GATE exam for the past 2 years. Can anyone tell me how about the placement in IIT's for m.tech in (microelectronics and vlsi or electronics related discipline). Some of them are telling like placement is very rare for m.tech electronics. Also the placement details in IIT websites are not true. Is that so ? can any one help us regarding this.
Why capacitor bank is not neccessery to switch on,pls answ me with formula
what is effect of 5amp fuse on 2mva pry protection of transformer
What are series and parallel isolators?
Hi all, please could anybody give me a suggestion about Electrical designs and calculations .. what text book should i follow as i am a trainee engineer and here work going not so favorable to me so please help me friends .. A small discription about my work which is going here is all about Electrical designs like cable sizing, lighting, lightning, Gensets sizing, motor sizing, transformer sizing, generator sizing, circuit breakers, PDB MCC PCC SLDB MLDB panels, Single line diagrams mainly, substation desings, cable routing and layouts, reactive power compensations, power factor improvement, voltage drop calculations, power generations, power transmission, power distributions all calculations i need .. please please if anybody experienced with this problem and got a solution then please help me .. just i need an apt text book for these all calculations and designs ..
On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Current: 693A Voltage:294/20KV OLTC Type: T III Y1000 110/c 12193w Max Operation Current: 295A Step Voltage: 550V Arrangement in Tx windings: Y Connection Problem: Damage of Unit 1 Generator Transformer On Load Tap Changer (OLTC) Description of Incident: 9.00 a.m. :- Generator No Load test on excitation system started 10.30 a.m :- Carried out AVR change over test 11.30 a.m :- Preparation for Generator Manual Synchronizing test 12.00 a.m :- Manual Synshronizing test started. Observed incoming generator voltage higher than running voltage. CECR operator operated Generator Transformer OLTC to bring down the incoming generator voltage 12.03 a.m :-Generator Transformer abnormal alarm operated at Gen.Control Desk (CECR) CECR operater at Generator transformer bay informed that the transformer oil splashed out from OLTC. CECR operater informed that he heard explosion inside OLTC. Observed Oil level & Oil Flow alaram operated at Tranformer local annunciator. 12.05 am :- CECR operator 'Open Gen Field Breaker” 12.10 a.m. :- Elec1 team inspected the OLTC and found the OLTC rupture disk was broken and oil spilled at OLTC area. - Elec1 found the OLTC top cover bulging. Do anyone know why and possibility cause happen in this OLTC.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)