For having nonavailablity of 10 Amps fuse, a lineman replace
the same with 5Amps two strand, Do he correct ?
Answers were Sorted based on User's Feedback
Answer / gravityguru
connecting them in series will not serve the purpose but
connecting them in parallel will serve our purpose..
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / nagaraj pole
both are same rating but thing is only rating lable changed
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / santosh kawade
No.
If 10 amps fuse not available replce the same with 5 amps
two strand is not correct.
Because while connecting two strands in parallel current
distribution between them will not be equal and if one fuse
fail above 5 amps the other automatically fails
subsequently.
Santosh Kawade
9224 69 3116
Is This Answer Correct ? | 1 Yes | 4 No |
Describe Non I.S. Earth System and why is it used?
Why let through energy not considered for ACB breaker while cable sizing?
In our factory so many iron pillors are exists for supporting the shed/Hangar. If do more no of earthings at one piller instead of doing more earth pits in many locations and running earth strip around the hanger, I can save the money. Please suggest this method is acceptable as per Is specifications though the Earth resitance of the farthest piller is with in the limits as per IS specifications.
help me with the question that might be ask on the interview for technical position
how step up transformer step up the voltage and what is the reason behind it?
As you achieve greater success with the company after some years, Will you like to be a share holder in our company?
How to calculate the Short Circuit Impedance in Transformer?
How will you justify IR value and Charging voltage of any motor,transformer and Cables.......???? . . . . . . . . Plz tell me any body Baljeet Singh, engineer_89@refiff.com
Describe the test procedure to determine the vector group
WHat is the general checks required for Dry type transformers
It is being often experienced that due to single phasing fault of any source transmission line of any closed loop synchronized circuit all the power transformers with primary stared trips but the power transformer with primary delta wont, why ?
What is the minimum insulation value required for a cable between phase to phase and phase to earth of 380 Vac 50Hz circuit, having load arround 800 amps.