what is surge arresters ?........
Answers were Sorted based on User's Feedback
Answer / minalverma
surge arresters are also called as lighting arresters.They
are always connected in shunt to the equipment to be
protected.They provide a low impedance path for the surge
current/surge voltage to the ground.
when the lightening ocurs,there is a voltage around some
thousands of voltage on line (35000v to 5000v) for a
fraction of second which is very high more than enough to
damage all the equioments in the grid connected to it.so
when a lightning arrester is connected then it provides a
low impedance path such that all that high voltage is
directed towards the earth resulting the protection of all
the equipments connected to the grid.
| Is This Answer Correct ? | 10 Yes | 0 No |
Surge means sudden increament. In electrical ckts, due to
some internal & external faults. sometimes the fault may
induce the overcurrent or overvoltage. to protect the
system from this spikes, we use the surge arresters.
| Is This Answer Correct ? | 5 Yes | 0 No |
the surge arresters is sudeen rise in voltages or current
in line thats limit by surge arresters
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / mahesh sali
surge arresters is protection device protect from lighting
stroke , It help to discharge the lightning surges into the
earth by providing low resistance path , save the
electrical equipment against the Lighting
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gurpreet singh
surge arrestor is the device which can only absorbs the
surges(high current) occuring due to any type of
symmetrical or unsymmetrical faults or due to lightening
strokes.it contains earthing resistors which can earth the
extra high current by providing a low resistance path.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sudharvino
means that,To limit the current or voltage according to the
specification and not allow to rise the limit............is
it..............
| Is This Answer Correct ? | 0 Yes | 2 No |
How to calculate motor current for 3 ph & 1 Ph motor from KW rating?
as per IE stranded what is max voltage between neutral to earth. 100 kva transformer neutral solid earth. min and max values i need to ans for RTI question
if we keep frequency constant can we cal a synchronous generator as a dc generator
What is mean CT Saturation? How to calculate?
Why is it not possible to operate a star-delta transformer in parallel with delta-delta transformer?
3 shows a 415 V, 3-phase generator supplying a 3-phase 415/110 V transformer. Draw the individual and combined impedance diagrams to a base of 10 kVA. Determine the system fault kVA and the fault currents at the 415 V and 110 V busbars for short circuit faults on the transformer input or output terminals. Work in p.u. values of impedances.
when we have to use UPF wattmeter and LPF wattmeter? what is the difference between UPF and LPF wattmeter in terms of construction?
what is the advantage and disadvantage of billing in kwh and kvah by electricity board .
why generator efficiency is more in swinburnes test?
why we use 6nos of C.Ts on 11kv incoming?
i want wipro vlsi placement pattern please send me
As all us know that the capacitor panel is connected to improve the power factor when it is PF is low. whether we can connect the capacitor panel on D.G. side(? If it is yes means why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)